Ifc circulators with zone valves
RayH
Member Posts: 98
in Oil Heating
Does a system that has zone valves and no flow check require an Ifc circulator
0
Comments
-
Usually no, but it depends on how its piped. Are you getting ghost flow in the zones not calling for heat?steve0
-
If your zone valves are controlled by your t-stats directly and you have a indirect hot water tank that has DHW Priority enabled, the zone valves will remain open when the indirect tank circulator is running.
If you didn't have a flow-check on/after the spaceheating circulator in this case you would get reverse flow through the spaceheating loops with energized zone valves.
0