Does a system that has zone valves and no flow check require an Ifc circulator

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    edited January 2018
    Usually no, but it depends on how its piped. Are you getting ghost flow in the zones not calling for heat?
    steve
  • NY_Rob
    NY_Rob Member Posts: 1,370
    If your zone valves are controlled by your t-stats directly and you have a indirect hot water tank that has DHW Priority enabled, the zone valves will remain open when the indirect tank circulator is running.
    If you didn't have a flow-check on/after the spaceheating circulator in this case you would get reverse flow through the spaceheating loops with energized zone valves.