Equalizer transition point
Options
info43
Member Posts: 51
Hi all!
My equalizer and boiler-return pipe will be 2” and my wet return is 1 1/2” where is the proper place to make the transition?
Thanks for reading my question.
My equalizer and boiler-return pipe will be 2” and my wet return is 1 1/2” where is the proper place to make the transition?
Thanks for reading my question.
0
Comments
-
I would say on the riser after the header turns down ( full header size through the last turn ). There may be other options but that one is safe.hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0 -
at the hartford loop 2" below the bottom of gauge glass
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0 -
I misread this is correct , equalizer to wet return.newagedawn said:at the hartford loop 2" below the bottom of gauge glass
hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0 -
**edited**
Thanks, 2" below the bottom of gauge glass would be after the 2" short nipple, so either at the Tee in yellow or midway between the Tee and the elbow above.
0 -
Use a reducing 90 or a bull head Tee (1.5 X 1.5 X 2). There should be a close nipple there, as shown, to prevent water hammer.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Thank you all for the advise!0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements