EFM 520 Highboy
Coalsteam
Member Posts: 2
Hello all,
New to the site. I'm about to embark, weather permitting, on a steam boiler install. I bought a 1953 EFM "Highboy". It has a Fitzgibbons boiler. My house has a one pipe steam system. My question is what size should my header be? The boiler currently has a 2" bushing in it from a previous hydronic system. Will 2" work for steam? Thanks
1. measure the installed radiation and determine the load
2. . Select your new boiler
3. Download or get a copy of the boiler manual and pipe it the way the manual shows.
4. That's a start, also check your venting0 -
@EBEBRATT-Ed , The new boiler is a 1953 EFM Highboy0
Is the old one leaking?
What is on label of the new one.
Rated for steam and water pressure?
Taps for sight glass? LWCO?0 -
The Smithsonian called, one of their boiler displays is missing!0
EFM builds a lot of new DF520 coal stokers every year and they can burn both Anthracite and Bituminous rice coal.0
The EFM manual is sadly lacking any information about pipe size for the header. I suggest looking at the installation manual for a current steam boiler, like a Weil McLain Gold. You will see that they recommend a minimum pipe size of 2.5" for that EDR. If you are going to take on removing that 2" bushing, you might as well run a 3" riser & header.0