EFM 520 Highboy

Hello all,
New to the site. I'm about to embark, weather permitting, on a steam boiler install. I bought a 1953 EFM "Highboy". It has a Fitzgibbons boiler. My house has a one pipe steam system. My question is what size should my header be? The boiler currently has a 2" bushing in it from a previous hydronic system. Will 2" work for steam? Thanks

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,279
    Are you sure your "new" boiler can handle steam?
    How many taps are in it for supply?
    You need to know your connected EDR.
    What is the existing steam boiler.
    Pictures of both would help.
    RomanGK_26986764589
  • Coalsteam
    Coalsteam Member Posts: 2
    Yes its H-stamped.
    One tap for supply.
    EDR - 360sq/ft
    Oil
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    1. measure the installed radiation and determine the load
    2. . Select your new boiler
    3. Download or get a copy of the boiler manual and pipe it the way the manual shows.
    4. That's a start, also check your venting
  • Fred
    Fred Member Posts: 8,542
    @EBEBRATT-Ed , The new boiler is a 1953 EFM Highboy
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Is the old one leaking?
    What is on label of the new one.
    Rated for steam and water pressure?
    Taps for sight glass? LWCO?
  • John Mills_5
    John Mills_5 Member Posts: 952
    The Smithsonian called, one of their boiler displays is missing!
  • leonz
    leonz Member Posts: 1,339
    EFM builds a lot of new DF520 coal stokers every year and they can burn both Anthracite and Bituminous rice coal.
  • Robert_25
    Robert_25 Member Posts: 549
    edited December 2017
    The EFM manual is sadly lacking any information about pipe size for the header. I suggest looking at the installation manual for a current steam boiler, like a Weil McLain Gold. You will see that they recommend a minimum pipe size of 2.5" for that EDR. If you are going to take on removing that 2" bushing, you might as well run a 3" riser & header.