Old gravity fed boiler
But you would still bring new PEX from each rad to the boiler room?0
The ready-made manifolds are pricey, but they do offer a lot of features.0
I was actually leaning towards maintaining the direct return (with 1” or 1.5” fostapex) rather than converting to a home run because there are about 20 rads which means I’d have to run 40 lines through a block wall that separates my boiler room from the rest of the house. Is there a significant advantage that should make me rethink that?0
Other issue is that this is pretty much the worst time for me to be doing this with temps dropping by the day. Would a pro be able to swap out the steel pipe for fostapex for 20 rads in just one day so I don’t have to go without heat?
I was thinking that if the lines were all pre run then the actually swap and rad connections might be possible in one day but maybe not?0 -
Any thoughts on downtime for a pro to swap out the steel pipes?0
$$$$$$$$$$$$$$$$$0
This is the kind of project that really should wait until heating season is over. During heating season, the need to get the heat back on ASAP has the high chance of resulting in unacceptable compromises.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg1 -
I agree with @Brewbeer. Murphy’s law will raise its ugly head about the time the system is drained, and taken apart.
Home run to a manifold with flow meters, and I like trvs. Gives control to each rad,eliminates thermostats. A project for summer when time is not of the essence.1 -
One day? Probably more like one week.Jsbeckton said:Other issue is that this is pretty much the worst time for me to be doing this with temps dropping by the day. Would a pro be able to swap out the steel pipe for fostapex for 20 rads in just one day so I don’t have to go without heat?
We're doing this very thing on a system with 16 rad's and that's what it's taken us. We did move some of the rad's and had 4 new total runs, but no way close to happening in a day.
Bob Boan
Wow a week! Is That even if you had the mains all pre run and the pex adapters all ready to screw on to the steel pipe?
I was thinking that the actual swap would take maybe a man hour per rad since there are easily accessible unions. There are only 10 rads on the steel pipe so with two guys it seems doable but maybe not. I understand that there is per-work and post-work but just want to limit the actual time w/o heat.0 -
Yes, some of the work could be done while the heat is still on, like installing manifolds and pulling PEX from the manifolds to the locations of each of the risers. But disassembling and reconnecting 20 risers, AND removing and installing a new boiler in one day seems fraught with potential snags. A 100+ year old gravity system isn't going to come apart without fighting and complaining, and possible breaking in a spot or two.
@Gordy 's suggestion that you home run each radiator with PEX to a manifold is a good one. If you do try to pull this off mid heating season, with the home run method, you could probably get most of the radiators up and running and deal with any problem radiators on subsequent days. If you try to zone or manifold radiators to common mains, you could end up being heatless for longer than desirable or end up with undesirable compromises.
A home run system will also provide superior adjustability and comfort vs. a zoned system.
Can you post some photos of the piping where the risers are connected ?Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0 -
The 2.5” pipes go through a brick foundation wall. It would be a mess trying to get 40 all the lines I would need for a home run system so I was thinking 2-3 zones with zone valves.0
I've faced bigger obstacles than that concrete wall. I wouldn't let that deter me from doing it the best way. Hire someone to come out and punch a few holes through it so you can run your pipe.0
That’s why they make core drills, and hammer drills. Piece of cake.0
There have been some recent posts of systems that have been sorta/kinda zoned differently from the original gravity piping and ended up in the heating hell section.
IIWM I would connect each rad to a manifold and have the ability to adjust flow to each.
You can have manifolds remote from the boiler room, you don't have to bring every tail to one location.
You could have a manifold for each zone with a Tstat control for that manifold. Endless possibilities.
But you need someone on site who is familiar with all this. IMO1 -
What is the advantage of a home run over a few zones with a direct return if the rads themselves already have balancing valves or I added them to the risers?
I can certainly get through that wall, just want to make sure that it’s going to have some kind of benefit. Those of you that are drilling cores, are you reinforcing the holes you drilled or just banking on them not interfering with the integrity of the wall? The current system has pipes that were cemented into the wall and now the steel runs through those pipes so there is no compromise of the wall.0 -
The sleeve around the existing mains isn't there to reinforce the wall, it's there to keep the mains from contacting the concrete, which would cause corrosion. If the wall is concrete or concrete block, a couple of 6 inch cores shouldn't make a difference, but if you post another photo of the wall further back also showing the framing above we could get a better look.
The advantage of the home run vs zoned system is that the home run system will definitely wok and work well if sized correctly.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
Are you an engineer?0
I'm a geologist and partner in an engineering firm and one of our specialties is foundation design and failure assessment.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
Cool..........Over the years, I've seen rather large holes put in foundations(residential), and years later there is no sign that the structural integrity has been compromised. I was just wondering if boring some holes would actually hurt the integrity. I feel that sleeving the holes is probably more for aesthetics than anything else. I understand there is reasons why you really don't want to do it. Especially, an exterior foundation. But I believe he is talking about one that is no longer exterior.0
I actually am a mechanical engineer and I’d be less worried about cutting holes if this were part of a larger wall but it’s a small section next to a doorway. There is 2 stories of brick stacked above this.0
Take a look at above the door. Look what is holding up two stories of brick there.Jsbeckton said:I actually am a mechanical engineer and I’d be less worried about cutting holes if this were part of a larger wall but it’s a small section next to a doorway. There is 2 stories of brick stacked above this.
Why not just run some 1.25" pipe though the wall, and put your manifolds on the other side ?Jsbeckton said:I was actually leaning towards maintaining the direct return (with 1” or 1.5” fostapex) rather than converting to a home run because there are about 20 rads which means I’d have to run 40 lines through a block wall that separates my boiler room from the rest of the house. Is there a significant advantage that should make me rethink that?
Looks like there is a beam on the other side of that short wall segment right of the door. Reusing the existing main holes with remote manifolds seems like a good option.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
Look at this job where I just posted some more pics:Jsbeckton said:Wow a week! Is That even if you had the mains all pre run and the pex adapters all ready to screw on to the steel pipe?
https://forum.heatinghelp.com/discussion/163504/gravity-system-boiler-replacement#latest
Bob Boan
Until we know what the needs are for piping to the rads in question which would dictate the size of the supply, and return to a remote manifold no need to worry about this wall.
I can safely say you won't need that size existing pipe now. So use the sleeves. Those sleeves wer put in after a hole was made, and patched around them.
To the OP want to see a nice home run install view this thread https://forum.heatinghelp.com/discussion/163504/gravity-system-boiler-replacement#latest0 -
@GordyGordy said:Until we know what the needs are for piping to the rads in question which would dictate the size of the supply, and return to a remote manifold no need to worry about this wall.
Great minds think alike.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
The other side of that wall will be finished.0 -
> @Gordy said:
> when We say home run your radiators it does not mean that all the individual rad lines need to come back to the boiler area.
> Remote manifolds are your friend. You pipe supply, and returns to the manifold.
> With the wall in question how many rads are on the side away from boiler location?
There are 8 rads down that side.0 -
Ok, I know the room loss so would the next step be to calculate the flow rates needed for each rad? I have some in wall rads as well as baseboard. Is there a good resource that shows the heat output of various types of rads for different flow rates?
If I can get this done then it just seems a matter of determining the flow rate needed to each zone so I can determine the size of the mains I need.0 -
I did look at that other thread, nice work!
Does a home run setup mean that I need a circ pump on each manifold? I was originally thinking one variable speed pump and zone valves.0 -
Going to need the heatloss of the rooms. The type of CI rad (thin tube, column) so you can calculate the EDR (equivalent direct radiation) of the radiator supplying the rooms load. Type of baseboard, and how many feet supplying the load in those associated rooms. There are output charts available at different water temps.
Then you can figure out the tube size supplying the rad, or baseboard, the flow rates. Then you size the circulator.
The EDR survey also lets you see what water temps you will need at design day. Whether or not radiation is balanced to the loads. In other words will an average water temperature of 160 be sufficient to meet the load in all radiated areas.0 -
Take pics of rads, and baseboard we can help you decipher types.0
It may be possible to use one circ, but we need the info requested to determine that.Jsbeckton said:I did look at that other thread, nice work!
I used two circs on that job because the owner wanted two zones. The risers from the gravity system were intentionally smaller for the upstairs to force more water to the downstairs rad's. Pumping the system causes the opposite effect: water flow wants to go to the downstairs rad's because there's less resistance to flow. Using separate circs eliminated the issue, though it may have been possible to do with the flow setters.
Bob Boan
Here are some photos of the different types of rads I have.0
- 86.8K THE MAIN WALL
- 56 Biomass
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 69 Pipe Deterioration
- 955 Plumbing
- 385 Solar
- 15.3K Strictly Steam