Tried to replace my thermostat, made things worse...
steamsosteamy
Member Posts: 7
in Gas Heating
I had an issue where my thermostat was no longer working so I went to replace it. I must've messed up the wiring because when I turned on the new thermostat, I noticed smoke coming out of whatever it is in the pictures I included below. This thermostat controls my basement heat which is water/baseboard gas heat. I disconnected the new thermostat and I think it would be best if I call a professional for this. Does anyone know what the below picture is? Would it be better to call an electrician or heating specialist?
That's a switching relay with an internal transformer. Did the circuit breaker trip?
Did you do any work on that box during the t stat change0 -
The circuit breaker did not break. Once I noticed the smoke I did kill the circuit breaker to remove the thermostat. I've never worked/touched that switching relay box.Leon82 said:That's a switching relay with an internal transformer. Did the circuit breaker trip?
Call a heating professional. You may need a new relay, t-stat or both. Most electricians aren't going to know what they are looking at.
You need a competent heating professional. While you might be able to find an electrician to work on it, it's part of your HVAC system. Try the blue bar above, "Find a contractor", or tell us where you're located.0
Sad but true, most electricians don't know controls.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
As a washed up electrician, I have to say that controls are not an electrician's responsibility. While many electricians could figure it out (given time), a boiler technician should recognize the function of the controls nearly immediately, if not the particular brand/model number off the device.
TL;DR: call an HVAC technician experienced with the style heat you have for trouble with anything attached to it
When you have someone come out, point this out to them, as well as the toasted coil in the relay above it.
Thanks, will do. Would that coil be part of the relay box?STEVEusaPA said:When you have someone come out, point this out to them, as well as the toasted coil in the relay above it.
Edit: What is that thing you circled in the image?0 -
You changed your wall T-stat? Was there only 2 wires coming out of the wall? If so you could most likely not screw anything up with just those 2 wires.
The picture with the circled wires......by code no bushing is required on the male threads above the locknut.
That scarring of insulation is a result of bad installation.
That is probably MC cable with solid wire.
IMO the best wiring for boiler controls/power is stranded #14 in 3/8" flex conduit. Takes longer but you are not having solid # 12 copper wire putting stress on terminals.1 -
4 wires, 2 were capped as my prior T-stat was only using 2. The older T-Stat was battery powered (batteries were replaced before realizing it no longer worked).JUGHNE said:You changed your wall T-stat? Was there only 2 wires coming out of the wall? If so you could most likely not screw anything up with just those 2 wires.