Tried to replace my thermostat, made things worse...
I had an issue where my thermostat was no longer working so I went to replace it. I must've messed up the wiring because when I turned on the new thermostat, I noticed smoke coming out of whatever it is in the pictures I included below. This thermostat controls my basement heat which is water/baseboard gas heat. I disconnected the new thermostat and I think it would be best if I call a professional for this. Does anyone know what the below picture is? Would it be better to call an electrician or heating specialist?
  • Leon82
    Leon82 Member Posts: 684
    edited November 2017
    That's a switching relay with an internal transformer. Did the circuit breaker trip?
    Did you do any work on that box during the t stat change
  • steamsosteamy
    steamsosteamy Member Posts: 7
    The circuit breaker did not break. Once I noticed the smoke I did kill the circuit breaker to remove the thermostat. I've never worked/touched that switching relay box.
  • STEVEusaPA
    Call a heating professional. You may need a new relay, t-stat or both. Most electricians aren't going to know what they are looking at.
  • ratio
    ratio Member Posts: 4,173
    You need a competent heating professional. While you might be able to find an electrician to work on it, it's part of your HVAC system. Try the blue bar above, "Find a contractor", or tell us where you're located.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,644
    Sad but true, most electricians don't know controls.
  • ratio
    As a washed up electrician, I have to say that controls are not an electrician's responsibility. While many electricians could figure it out (given time), a boiler technician should recognize the function of the controls nearly immediately, if not the particular brand/model number off the device.
    TL;DR: call an HVAC technician experienced with the style heat you have for trouble with anything attached to it
  • STEVEusaPA
    When you have someone come out, point this out to them, as well as the toasted coil in the relay above it.
  • steamsosteamy
    Thanks, will do. Would that coil be part of the relay box?
    Edit: What is that thing you circled in the image?
  • Leon82
    That's a neutral wire that has seen better days. There should be a plastic nut on the end of that connector so the wires don't touch the metal.
    I didn't even notice the coil on top, its done
    Canucker
  • JUGHNE
    JUGHNE Member Posts: 11,508
    You changed your wall T-stat? Was there only 2 wires coming out of the wall? If so you could most likely not screw anything up with just those 2 wires.
    The picture with the circled wires......by code no bushing is required on the male threads above the locknut.
    That scarring of insulation is a result of bad installation.
    That is probably MC cable with solid wire.
    IMO the best wiring for boiler controls/power is stranded #14 in 3/8" flex conduit. Takes longer but you are not having solid # 12 copper wire putting stress on terminals.
    Solid_Fuel_Man
    HVACNUT Member Posts: 7,191
    Its possible the 845 was the problem to begin with. Agree with all from above. Get a heating pro. He might even recommend bringing all the zones into one, multi zone control board.
    Solid_Fuel_Man
  • steamsosteamy
    4 wires, 2 were capped as my prior T-stat was only using 2. The older T-Stat was battery powered (batteries were replaced before realizing it no longer worked).