I have a customer with a cc150. 2 months old. Ran good for about 3 weeks. Now it won’t recycle and locks out with a 4E code - means flame failure or loss of signal. Found a cut in the ignition cable. Thought “ha this is the problem” NO. Still acting up. Spoke w factory re this. Natural gas fired. 9” inlet. Drops to 6.9”WC on forced high fire. Clocked the meter to 132,061btu. Adjusted mixture w analyzer to midpoint factory settings 45 ppm CO. Book says <100ppm. Unit fires drops flame does this twice and on the third time seems to ramp down and stay rectified. Runs for 3 hrs or so then locks out.
Mount Pleasant Plumbing and Heating Inc
0 ·
Comments
Been reliable.
Tell me more on the install...
Venting?
Gas pressure steady? New or old meter/ regulator?
Any CSST?
Gas pressure was good.
I did a total teardown.
Cleaned it head to toe... which as you know is very easy to do.
Cleaned probe and igniter.
I checked both low and high fire and made just a ever so slight adjustment.
Its been great since.