Hello -
I am replacing my original pressure gauge (no longer functioning/troubleshooting complete to ensure it's just the gauge). Current gauge was installed connected to top of sight glass with no pigtail - see attached picture where line goes up to the left. Do I need a pigtail for protection, or can I just replace the gauge at the end (assuming sight glass water and/or lwco tube protects it? Couldn't find anything via search.

Also, my system runs greats, and I have learned over the years (a lot through this site) of how the steam systems work.
Thank you, Keith
I am replacing my original pressure gauge (no longer functioning/troubleshooting complete to ensure it's just the gauge). Current gauge was installed connected to top of sight glass with no pigtail - see attached picture where line goes up to the left. Do I need a pigtail for protection, or can I just replace the gauge at the end (assuming sight glass water and/or lwco tube protects it? Couldn't find anything via search.

Also, my system runs greats, and I have learned over the years (a lot through this site) of how the steam systems work.
Thank you, Keith
0
Comments
-
A pressure gauge needs a pigtail to protect the gauge from live steam. The pressuretrol also needs one.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thank you. Just trying to understand how it hasn't had a pigtail for all these years (I think original to the Pennco boiler in the 1930s), and worked just fine. And why it would be run off a tee from the sight glass?0
-
The original gauge may well have been steam rated, you can still get them but they will cost a lot more. The gauge can be run from anyplace that is above the boiler water and the higher up it is the better.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Did the original gauge have an internal siphon? It should say that somewhere on the gauge if it did. Internal siphon doesn't need a pigtail.0
-
Gauge is an original Marshalltown, and don't see "internal siphon" on it anywhere. See picture. I didn't even know they made gauges rated for steam - curious now - can you suggest a brand/website for more research? I've been through most of the brands - Wika, Ashcroft, etc.
To add a pigtail, I can add one inline (and add water) to the existing sight glass to gauge connection, or I can tee off of the pigtail that is in place for the pressuretrol.1
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements