Pressure Gauge off Sight Glass
kredmore
Member Posts: 53
Hello -
I am replacing my original pressure gauge (no longer functioning/troubleshooting complete to ensure it's just the gauge). Current gauge was installed connected to top of sight glass with no pigtail - see attached picture where line goes up to the left. Do I need a pigtail for protection, or can I just replace the gauge at the end (assuming sight glass water and/or lwco tube protects it? Couldn't find anything via search.
Also, my system runs greats, and I have learned over the years (a lot through this site) of how the steam systems work.
Thank you, Keith
Thank you, Keith
A pressure gauge needs a pigtail to protect the gauge from live steam. The pressuretrol also needs one.
3PSI gauge0 -
Thank you. Just trying to understand how it hasn't had a pigtail for all these years (I think original to the Pennco boiler in the 1930s), and worked just fine. And why it would be run off a tee from the sight glass?0
The original gauge may well have been steam rated, you can still get them but they will cost a lot more. The gauge can be run from anyplace that is above the boiler water and the higher up it is the better.
3PSI gauge0 -
Did the original gauge have an internal siphon? It should say that somewhere on the gauge if it did. Internal siphon doesn't need a pigtail.0
Gauge is an original Marshalltown, and don't see "internal siphon" on it anywhere. See picture. I didn't even know they made gauges rated for steam - curious now - can you suggest a brand/website for more research? I've been through most of the brands - Wika, Ashcroft, etc.
To add a pigtail, I can add one inline (and add water) to the existing sight glass to gauge connection, or I can tee off of the pigtail that is in place for the pressuretrol.1