Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Ultra 105 stuck on stand-by

Options
Rpb
Rpb Member Posts: 1
I can't seem to get my boiler off of standby. This Spring there was a power outage and sort of a brown out and since then when I put up the thermostat the circulating pumps go on but it doesn't fire up.

Comments

  • Leon82
    Leon82 Member Posts: 684
    Options
    What is the temp outside?
    Some modcons will block heat calls if the outdoor sensor is above a certain temp set in the parameters
    kcopp