Ultra 105 stuck on stand-by

Rpb
Rpb Member Posts: 1
I can't seem to get my boiler off of standby. This Spring there was a power outage and sort of a brown out and since then when I put up the thermostat the circulating pumps go on but it doesn't fire up.

Comments

  • Leon82
    Leon82 Member Posts: 684
    What is the temp outside?
    Some modcons will block heat calls if the outdoor sensor is above a certain temp set in the parameters