Combining Zones with Taco Relay
Essentially causing both zones to call for heat off 1 thermostat?
Yes, you can do that.
It might not be W to W.
I believe, but not positive, with Taco, you need to jump the right side terminal on zone 1 to the right side terminal on zone 2.
If that doesn't work, do left to left.
Why are you combining zones though? Will the "jumped" zone over, or under heat?0 -
Boiler is a bit over sized for the house, so I'd like to heat the whole upstairs as one to avoid short-cycling. The jumped zone may over heat a bit. The zone 2 is for both upstairs bedrooms. Zone 1 is for the kitchen and dining/livingroom. I'm not really sure how much overheating will be a problem until I try it. With the taco control it's my understanding the R is the 24Volts out and White is the signal wire coming back. And yes, I believe W is the right-side terminal. Just don't want to blow the thing up! So you've seen this done before?HVACNUT said:Yes, you can do that.
Connect "W" from the zone thermostat that you want to control both to "W" on the other zone. Remove the red and white wires going to the t'stat that you want to disable.Bob Boan
> Yes. Switching is done on the power side through the thermostat. You'll get a 24v reading across R and W (TT) from the transformer coil when there's no connected load. But it doesn't change what your doing.
> Ive done it numerous times on a temporary repair basis.0 -
Update: I just checked my SR506. It's older, and has cube relays, but on mine, the left terminals are the load side of the thermostat circuits.0
I'll have to double check mine..Now you have me guessing. I just assumed W would be load side. So would I just check each R/W terminal to common to find which one is the line?HVACNUT said:Update: I just checked my SR506. It's older, and has cube relays, but on mine, the left terminals are the load side of the thermostat circuits.
> Yeah, you can check it. Or you can just jump the left side, if that doesn't work, jump the right. You won't short anything.
Mine is designated TT, not RW.
Like I said, mine is older, so yours is a newer revision.
We don't use Taco where I work, so I don't run into them too often.0 -
You're over-thinking this. It doesn't matter whether "w" is on the left or right; it's still the switched terminal and "r" is still the hot side from the transformer. Just connect "w" to "w" and remove the wires going to the stat that will not be used.
If the terminals are labeled "t t", then you'll need to ring them out.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.-1 -
@HVACNUT Just a question, don't care either way. Is there a reason why you don't use the Quote button when replying to a person? It makes it much easier to read than using these '>'
I'm trying to figure out what the quote button is and how to use it.STEVEusaPA said:@HVACNUT Just a question, don't care either way. Is there a reason why you don't use the Quote button when replying to a person? It makes it much easier to read than using these '>'
WOW
bob said:
WOW
I was wondering also.......so click into the comment bar....go up to some posting and click Quote.....is that right?Ironman said:Connect "W" from the zone thermostat that you want to control both to "W" on the other zone. Remove the red and white wires going to the t'stat that you want to disable.
I'm using a phone, so it's set up a little different than the main site"quote, unquote".
Sorry for the confusion.0 -
I didn't know it was different. I never posted from my phone.
For you guys playing with Quote, you can also highlight and delete some of it just so you see the relevant part. For example:
This:
Can get edited down to this:Ironman said:You're over-thinking this. It doesn't matter whether "w" is on the left or right; it's still the switched terminal and "r" is still the hot side from the transformer. Just connect "w" to "w" and remove the wires going to the stat that will not be used.
If the terminals are labeled "t t", then you'll need to ring them out.Ironman said:
If the terminals are labeled "t t", then you'll need to ring them out.There was an error rendering this rich post.
You guys are awesome and very quotable.0
- 109 Chimneys & Flues
- 975 Plumbing
- 386 Solar
- 17 Recall Announcements