reverse thermostatic valves?
Options
jumper
Member Posts: 2,488
The opposite of what car engine cooling systems had.
These open only when return water gets cool enough.
In this way delta T is maintained for each circuit.
Were such devices used in the fifties?
These open only when return water gets cool enough.
In this way delta T is maintained for each circuit.
Were such devices used in the fifties?
0
Comments
-
These are typically called return temperature limiters, they are definitely available for single loop radiant circuits (small loads) and in larger sizes they have other names, most then have remote sensors attached to the valve actuator via a capillary tube.0
-
Probably not available in the 50's. The Caleffi ThermoSetter, a thermal balancing valve, opens as temperature drops, to maintain a setpoint temperature.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 394 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements