A VERY Long Wall Hung Steam Radiator In A School Classroom
There were only a total of three brackets installed in 1924 holding this thing up in the first place. They originally anchored the three pieces of wood to the plaster-on-brick wall and mounted the hardware on the wood to hang the radiator.
Before we began work, we supported the radiator with temporary cribbing as shown in the video. Complicating the issue is the 1/2" return piping underneath the entire length of the radiator.
Years of "treasure" had been deposited behind the radiator preventing it from being brought to an upright position, and the debris had to be removed next.
Thanks @EBEBRATT-Ed !
Radiators like that were put in in the days when the windows were left open year round. Fresh air will keep our children safe!All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
And that, ladies and gentlemen, is one of many reasons why @Gordo is my partner.All Steamed Up, Inc.
Consulting3 -
Wow!
President
HeatingHelp.com0 -
Bruce was the best sideman Roy Orbison ever had.
3PSI gauge0 -
Oh my.Retired and loving it.0
He's referring to the "A Black and White Night" concert where a whole bunch of musicians, including Bruce, backed Orbison. It's out on DVD- highly recommended.BobC said:Bruce was the best sideman Roy Orbison ever had.
BobAll Steamed Up, Inc.
Consulting0 -
Both are great but there's no one like the big O0
What is the EDR on that bad boy?!0
Once we secured the radiator and were reasonably confident that it wasn't going to come crashing down on us, we disconnected the old 1" Dunham radiator valve and wrenched it off the supply pipe.
https://www.youtube.com/watch?v=odLe_3fVpq0
We then installed a new 1" Danfoss thermostatic radiator valve.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc5 -
A wrench designed today would break if you put a 3 ft pipe on it because the accountants would see to it that just barely enough steel was put into it to support it's designed handle length.
I've pulled old wrenches out of the trash and brought them home to restore. You do get some odd stares when your walking down the block with a rusty old two foot wrench on your shoulder but the neighbors know where to come when they need to borrow a pipe wrench.
3PSI gauge0 -
very cool..amazingly big radiator. How are you going to hold it with the broken supports?gwgillplumbingandheating.com
@gerry gill I'm glad you asked! Here is a video of the finished work on that radiator. Superstrut/Kindorf is wonderful stuff.
https://www.youtube.com/watch?v=6Y996sTRt1I
Also, please note the addition of the new 6" masonry lag screws.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc4 -
And here is the test.
The boiler is on and running. The steam is in the pipes, waiting impatiently.
The Danfoss TRV actuator is turned on... and, wow! There's the steam!https://www.youtube.com/watch?v=HIJbtcrWC6s
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc2 -
What is the edr of that rad?0
@kcopp : This particular radiator is 119 EDR.All Steamed Up, Inc.
@lchmb & @Grallert : That wrench is a "compound leverage wrench" made by Ridgid. The one shown is the smallest of that type, the model "S-2", part # 31375.
It is listed optimistically as being able to handle 2" pipe, but in reality, 1-1/2" is pushing it.
This wrench type uses a second class lever to apply tremendous torque in a tight space. "Second class" just means that the fulcrum point is at one end of the lever, the load is in the middle, and the force is applied at the other end.
The classic example of a second class lever is the wheelbarrow.
Classic examples of first class levers are a see-saw or a trebuchet.
An example of a third-class lever is the elbow and forearm.
I'm new to learning about steam heating. So the bizarre questions begin. Before supply steam is reconnected to the radiator, are radiators pressurized to blow out possible corrosion/sediment? I grew up on the East coast but have lived in California most of my adult life and don't see these old radiators out here. Thanks.0
The windows have mostly been upgraded, but there are still some originals. Also, there was no fresh-air intake to these rooms (though it was possible to add this capability to standard radiators) so they may have assumed some windows would be at least part way open.All Steamed Up, Inc.
Consulting0 -
If you have the radiator out, for some reason, perhaps in the yard, it is a good idea to hose them out and wash any crud out of them. Also, if you bought a used rad and are unsure of it's viability, pressurizing it before hauling it into the house and connecting it is the smart thing to do. If it is in place and you know it doesn't leak, there is very little reason to wash it out or pressurize it.bandito said:I'm new to learning about steam heating. So the bizarre questions begin. Before supply steam is reconnected to the radiator, are radiators pressurized to blow out possible corrosion/sediment? I grew up on the East coast but have lived in California most of my adult life and don't see these old radiators out here. Thanks.
I know those radiators well. We replaced 74 of them in two floors of a building in NYC a couple years ago. At the client's request, we put Charleston Pro rads in their place and did the whole job over three weeks working 7PM-1AM.
Time-and-a-half for all involved. Except me.
Most were about 7 feet long but a few were over 15.
Definitely a job for the young guys...
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
What did you do w/ the old rads?JohnNY said:I know those radiators well. We replaced 74 of them in two floors of a building in NYC a couple years ago. At the client's request, we put Charleston Pro rads in their place and did the whole job over three weeks working 7PM-1AM.
The building kept them.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Classes0 -
This is in the Midtown Academy, a charter school housed in the old Corpus Christi Catholic School which we're told closed in the 1970s. One of the more-typical radiators is this American Peerless 4-column monster in the front stairway. It has a new TRV and a rebuilt trap.All Steamed Up, Inc.
Consulting0 -
Here's how you add crossover vent traps to H-pattern F&T traps. This is one of two drop risers (this is an overhead or Mills system, with the steam main in the attic) at the far end of the building. The trap is a Nicholson high-capacity unit that we wanted to use up- the Barnes & Jones crossover traps do the same thing for much less money.
Consulting0 -
In the old gym, now used partly as a lunchroom/assembly room and partly as classrooms, we find wall radiators mounted high above the boiler's waterline.
You can see how the system evolved. In 1924, when this Dunham Vapor system was installed, it had a coal-fired boiler and was all one zone. At some point, probably when it was converted to oil, the gym zone was split off from the main building.
Note how there is a plugged tee on the drop riser just above the F&T trap. This originally fed the wall radiator. It also explains why the steam main for the gym was run below the dry return, which led to a problem..........
Consulting0 -
..... how do you drain the condensate from the main?
This obviously causes lots of banging. Not sure what arrangements they had originally but they are long gone now. We expect to install a couple F&T traps and run a new down-pitched dry return to the boiler room after school is out for the summer.All Steamed Up, Inc.
Consulting0 -
In the boiler room, we find a gas-fired Weil-McLain 6-88. When we got there it was set up to maintain pressure all the time, and we later discovered the main zone valve didn't always close. The actuators are Honeywell ML6984s, and they were daisy-chained from one transformer, which the instructions specifically prohibit. We replaced the bad actuator and separated the 24-volt power cables so each ZV had its own power cable.
I like to use these DPDT fan center relays since each one has a 40VA transformer. One pole of each unit's relay provides Series 20 control to the zone valve, and the other is wired as an on-off switch in the burner control circuit. In this way, the zone thermostat operates the zone valve and the burner at the same time, and the ZV power comes from the same transformer that operates the relay. The wiring will probably be rerouted at some point after a few other changes are made.
We also replaced and remounted both thermostats so they were not too close to radiators and were easier for adults to get to.
More coming!