Low voltage circuit problem. Thermostat works, zone valve works, no call for heat.
donaldmc
Member Posts: 35
But if I jump the TT in the Hydrostat the boiler fires up!?
I replaced the zone valve motor, checked all the low voltage wire nut connections(also soldered them), I have 24V at the transformer, the thermostat is working -every thing is fine for 2 to 3 days then the same problem again. I'm perplexed!
This is my third call to this unit for this same problem. Any help would be a blessing!
6 month old Biasi boiler with a NX burner, Hydrostat 3250-plus, Taco cirulator and zone valve.
Problem solved! Called the Hydrostat people-swapped it out- fixed. Still under warranty so I don't have to pay! All's well that ends well......the end switch in the zone valve was bad too. Hence the problem trying to diagnosis it.0
Which Taco model zone valve?All Steamed Up, Inc.
Consulting0 -
Honeywell 24v zone valve model #v8043e. The end switch was working intermittently, make diagnosis difficult.0
OK- that has a completely isolated end switch. Some Taco and B&G ZVs (and possibly others) do not, and if hooked up wrong they can burn out transformers.All Steamed Up, Inc.
Consulting0 -
Thanks for the info!0
The Hydrostat 3250 plus was giving a "code" when energized -I do not remember what it was- I was told by the tech at Hydrolevel to replace it. No cost, still under warranty.
Installed replacement - no code when turned on...0
