Low voltage circuit problem. Thermostat works, zone valve works, no call for heat.
donaldmc
Member Posts: 35
But if I jump the TT in the Hydrostat the boiler fires up!?
I replaced the zone valve motor, checked all the low voltage wire nut connections(also soldered them), I have 24V at the transformer, the thermostat is working -every thing is fine for 2 to 3 days then the same problem again. I'm perplexed!
This is my third call to this unit for this same problem. Any help would be a blessing!
6 month old Biasi boiler with a NX burner, Hydrostat 3250-plus, Taco cirulator and zone valve.
I replaced the zone valve motor, checked all the low voltage wire nut connections(also soldered them), I have 24V at the transformer, the thermostat is working -every thing is fine for 2 to 3 days then the same problem again. I'm perplexed!
This is my third call to this unit for this same problem. Any help would be a blessing!
6 month old Biasi boiler with a NX burner, Hydrostat 3250-plus, Taco cirulator and zone valve.
0
Comments
-
-
Problem solved! Called the Hydrostat people-swapped it out- fixed. Still under warranty so I don't have to pay! All's well that ends well......the end switch in the zone valve was bad too. Hence the problem trying to diagnosis it.0
-
Which Taco model zone valve?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Honeywell 24v zone valve model #v8043e. The end switch was working intermittently, make diagnosis difficult.0
-
OK- that has a completely isolated end switch. Some Taco and B&G ZVs (and possibly others) do not, and if hooked up wrong they can burn out transformers.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks for the info!0
-
-
-
The Hydrostat 3250 plus was giving a "code" when energized -I do not remember what it was- I was told by the tech at Hydrolevel to replace it. No cost, still under warranty.
Installed replacement - no code when turned on...0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements