What is it ?
bigred75
Member Posts: 4
I found this in between a union on a boiler gas line while replacing a leaking regulator. It was in the union close to the boiler.
What did you find?0
Looks like the Holy Grail to me.
All kidding aside your picture didn't post.-1 -
Looks like an orifice of some type. Maybe to change incoming pressure.0
I agree with @JUGHNE , I have worked on many Power Flame Commercial gas burners that had what they call a "side orifice".
In those cases, they brought the gas into the branch of a black tee. On the run of the tee was a plug. Removing the plug you would find a spring and an aluminum orifice, that the spring holds in place. The other run of the tee was gas into the burner.
They didn't use the orifice on all burners....depends on the firing rate.1 -
This Adams was a HP 800, it has a range from 300,000 to 800,000. This is accomplished with 2 orifice sizes included with burner; 3/8" and 37/64" sizes. Then adjusting the NG WC from 2" to a max of 5" WC. This burner is sized down now to 327,272 BTUH.
PS: these orifices are a thick aluminum disk that fit in a 1" union.
PPS: these are installed in the union fitting against the pipe nipple.
Not in the union itself. The OP orifice looks like a steam valve copper orifice plate......easy to distort installing on the nose of the union. FWIW0 -
These are 1 1/4" copper orifices that I drill out for steam valves to regulate input. The tortured one is a result of slipping while the union is tightened. Pretty heavy copper, new ones from Tungstall .0
@JUGHNE didn't know Tunstall had those, good to know0