Big Mouth Question for @Sailah
Steamhead
Member Posts: 18,193
We're working on a Hoffman system with a Return Trap, which uses 1" thermostatic end-of-main traps, piped like this:
These are piped so as to drain the condensate from the steam mains as well as to vent the air. We'd like to upgrade to the 3/4" Big Mouth Crossover Traps, but were wondering if the extra-large valve seats might wire-draw with such a light running condensate load (after the initial start-up when the mains are hot).
Thanks in advance for your thoughts.
Consulting
Consulting
I don't think they will wire draw. It's the same seat as their 1" trap just in a 3/4 body. Should be fine.Peter Owens
SteamIQ0 -
Wouldn't it be easier to just use the 1" trap instead of the big mouth in that case?
Our 1" trap is a 147A, won't provide the venting as a big mouth crossover but you avoid the hassle of getting to size. Could also rebuild what you have there with a new cage unit for the easiest solution.Peter Owens
SteamIQ0 -
You mean the MEPCO 3C?Sailah said:I don't think they will wire draw. It's the same seat as their 1" trap just in a 3/4 body. Should be fine.
Consulting0 -
Yes the big mouth is the 3C seat plug and disc in the 2E body. The crossover traps retain the brass seat while the vents have silicone.Peter Owens
SteamIQ0 -
Thanks much!All Steamed Up, Inc.
Consulting0