Noisy boiler
I have a Smith 8 series with a Carlin 99 and it is noisy,rumble up the chimney. Tried many nozzles,etc. Any suggestions.
    Jamie Hall Member Posts: 26,148
    Get the burner properly tuned with the appropriate test equipment.
    Grallert
  • STEVEusaPA
    Is this a new problem?
    EBEBRATT-Ed Member Posts: 18,169
    If combustion is good but noisy with a Carlin you can usually quiet the fire by a combination of adjusting the air band and the burner drawer assembly.
    If that doesn't help you may be able to down fire slightly to reduce the noise.
    Need a competent technician and MUST set up with instruments.
    HVACNUT Member Posts: 6,840
    HB Smith with the 99 Carlin is always noisy. I think it's the squat height of the block with the rear flue.
    What's the model# of the Smith? I'll post tomorrow the correct nozzle and starting points on the air and head settings.
    Ah the hell with it. Just put in a Riello.
    edited February 2017
    Haven't heard from you. Here's the setting for your boiler with the 99 Carlin. The columns after the nozzle are pump psi, air shutter, head position and air setting. Note 1 on the air setting signifies a single slot air band. Keep in mind these are just starting points. Final adjustments must be done with a combustion analyzer and 0 smoke.
    Never typically use Monarch nozzles (only on an original Blue Ray and praise god there aren't too many left) if you can't find one, you can use a W Delavan.
    Blue Ray, there's a flash back. John Cameron Swazy. Figured they would be all ripped out, gone or converted to yellow flame. Must be.......35 years
    Most have been converted or replaced in my area (Suffolk County Long Island NY) I'll be happy when they're all gone, converted or not. Heavy mothers too for a steel boiler.
