IBC boiler SL20-115G2 delayed ignition
electron
electron Member Posts: 14
Hi everyone.
I just had a brand new IBC SL20-115 G2 boiler installed recently. Ever since the installation, I noticed that during ignition, the boiler would make a "thump" sound. From reading, this seem to be delayed ignition problem.
The installer did some troubleshooting with the IBC tech on the phone, they measured the gas pressure and it was fine, and then they decided to replace the burner assembly.
However, problem was not solved, the noticeable "thump" noise is still there.
Anyone has any experience with this issue for this particular boiler? How did you fix it?
Thank you for reading
Sukhdeep
  • kcopp
    kcopp Member Posts: 4,612
    Is this LP or Natural gas? has this done this from the start?
  • electron
    Hi Kcopp,
    This is natural gas model and that it is doing it from the start.
  • kcopp
    I have never had that happen before. Check the igniter to see that it is in the opening and tight. Check your connections.
    How loud is the "thump"?
  • Abracadabra
    How's the draft? Combustion analysis been done?
    kcopp
  • kcopp
    That's a great question., I presumed that a combustion analysis was done on a new install.... What did they get for numbers?
  • electron
    Thanks you all for trying to help.
    Here is a video showing the "thump" noise.
    https://youtu.be/IsnrnX3sSs0
    I am not sure if an combustion analysis was done...i hope it is.
    How do i check if the ignitor is in the opening?
  • electron
    edited February 2017
    The boiler has so far logged 5 ignition errors and 8 ignition trials since it was installed 3 month ago
  • Abracadabra
    Does that boiler have spark or HSI ignition? If spark, make sure the gap is correct.
  • kcopp
    Spark... Still like to know what the combustion test #'s are.
    Ask the installer.
  • electron
    I believe the combustion analysis was not done.
    Can someone confirm that this noise is not normal?
  • kcopp
    It is lighting off a bit hard yes. It is not as smooth as I would like to see/ hear. Not "normal" but not super unusual.
  • kcopp
    Did you ever find out if the installer did a combustion test?
  • electron
    I think i better get someone to verify just in case.
    kcopp
  • rick in Alaska
    rick in Alaska Member Posts: 1,510
    I was having problems with the Triangle Tube boiler doing that also. It took quite a while for someone to figure it out. Turns out the gasket the ignitor goes through was too close to the ignitor and was "shorting"it out. They now have a new gasket they are using that has a tapered opening at the bottom that has fixed the problem. If yours is the same type of heat exchanger, you can pull the top off and taper the gasket back at the bottom just a bit to get more clearance around the tip of the ignitor.
    Rick
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    I had a NTI fire tube boiler doing the the same thing. It was a warped igniter. The had boiler been in service for five years or so. Replaced igniter and all is good. Strange that it did it right out of the box.
  • electron
    Hi Rick in Alaska,
    Thank you for your input.
    Sorry, I dont quiet get how the tapered gasket work. Can you please explain more detail on what I need to do?
    Hi Aaron in Maine,
    Yes, I am trying to figure out why a new boiler would do this.
  • rick in Alaska
    Not sure about your boiler, but the Triangle Tube boiler has a gasket on the top plate that the burner mounts to that is about 5/8" thick or so. It is under the top plate. The ignitor goes through this gasket. The gasket just has a straight through hole cut in it for the ignitor to go through. In order to fix the problem, you need to have the bottom of the hole tapered out away from the ignitor tip. You would need to take the top plate off to access the gasket, and then carefully carve away just a little bit of the gasket, but only on the bottom section. Leave the gasket intact where it meets the top plate.
    I just looked at the boiler and found the gasket is part number 140 in the manual.
    Rick
  • electron
    Hi Rick,
    Do you mean the two rods from the ignitor are touching the refractory causing it to be shorted?
    I had someone came in to do the combustion analysis.
    On High fire
    O2 = 4.3%
    CO = 36ppm
    Eff = 88.5%
    CO2 = 9.4%
    T-Stk = 160F
  • kcopp
    were those number at Low fire or High fire?
    Jamie Hall Member Posts: 26,776
    electron said:
    Hi Rick,
    I don't think that that's quite what @rick in Alaska meant -- although I can't be sure, never having seen it. I'd bet that what it might be is that the combustible mixture can't get at the ignitor quickly unless there is a bit more space around it.
  • rick in Alaska
    From what I understood, the ignitor will arc to the refractory. Not sure why, but that is how I understood it. After modifying the refractory, there have been no more delayed ignition problems on this job.
    Rick
  • electron
    Hi Kcopp,
    Those number are on high fire.
    Hi Rick,
    Did that boiler you worked on came with this issue since new?
  • rick in Alaska
    Yes it did. Triangle tube has now sent a different refractory (or so I was told by my rep) that has been modified. It was also kind of sporadic as to when it would mis-fire. But, the homeowner sure noticed it. Says it was like a cannon going off.
    Rick
  • electron
    My Ibc boiler would "thump" everytime it ignites.
    Ibc has referred a contractor who has replaced the ignitor and did the combustion analysis and made adjustment. Initially thought that has fixed it. However, it seem the thump is still there. Also, i just realized that if I open the cover and look through the sighting glass while it ignites, I can feel there is air/gas blowing out somewhere (from the micro explosion?) I will try to get IBC to send a representative out to look at it. Has requested previously but they wouldnt. After 3 contractors and many hundreds dollars, I think I need to get them to come out. I cant believe a brand new boiler would have problem like this.
  • electron
    Hi Rick,
    Does the ignitor from the Triangle tube also look like this?
    I suppose it's the other metal rod touching the refractory?
  • kcopp
    Where you out of?
  • rick in Alaska
    That is the same one. I don't think the rod touches the refractory, but I get the impression that it shorts out to it. Not sure how it can do that without going to the ground rod, but that is what I understand is what is happening. The trick is to get a little more clearance from the rod.
    Rick
  • electron
    Sorry, can I ask for a little clarification. So we make the refractory thinner from the bottom, not making the refractory hole for the ignitor bigger. Correct?
    HVACNUT Member Posts: 7,197
    The distributor who sold you or contractor the boiler should be able to provide you with the number for a regional rep. to meet with a reputable technician at the job site. The tech MUST have a digital combustion analyzer, manometer and true RMS multimeter.
    Sounds like a simple throttle adjustment on the gas valve, but after purchasing their product for bucu deneros, you deserve to have the Rep. come out to the job.
    Good luck.
    Teemok
    DO NOT ALTER THE REFRACTORY OR ANY PART OF THE BOILER.
    YOU'LL VOID THE WARRANTY.
  • electron
    Is there a way to limit the firing rate?
    Not familiar with that brand. Modulating? If there's an outdoor reset you can lower your design day temp. If DD is 10 degrees at 180, lower DD to -10 and she'll run at a lower rate throughout the band width.
  • aircooled81
    aircooled81 Member Posts: 205
    I think you should have a fairley high amount of sparks per second, enough that the ignitor will look like a constant arc...
    When the first stage for ignition takes place, what does the ignitor look like through the sight glass.
    Is it sparking once a second, twice a second?
    Fenwal posts the sparks per second on their website, for instance a 35-60 could spark 25/30 50/60 sparks per second.
    Could be the ignitor is not operating like it should, gas builds up to high of a volume before combustion takes place.
  • kcopp
    Any updates?
  • electron
    Thanks everyone for the input.
    IBC had an representative out, and the problem is fixed.
    I believe the angle of the ignitor was adjusted to spark closer to the burner.
    kcopp
  • evolvebg
    evolvebg Member Posts: 2
    Hi electron, I had the same problem with my G2. I'd love to contact you directly and discuss it if you are open to it. my email is jpavia@evolvebg.net. thanks!
  • MauriceC
    MauriceC Member Posts: 1
    I'm having the same issue, how did he adjust igniter to get closer?