Tri Tube prestige Solo E03
kcopp
Member Posts: 4,562
I have been asked to figure out an E03 nuisance lockout on a 6 yr old Triangle Tube Prestige Solo. It is the older control board w/ the mcba control.
Natural gas.
It is a commercial application. Area heated is above a parking garage and is fin tube run in the area above to keep the piping from freezing.
Unit will lock out every day or two w/o fail.
Manual says to check gas valve rectifier cable. Looked fine. Replaced... same problem.
Called TT.
TT tech support suggests the gas valve coil may be the issue. Replace That. Do a combustion test, Hi and Low fire All w/in spec.
Gas pressure is ok.. Static 6.23... 5.3 at hi fire.
Short of replacing the board (which seems unlikely the issue) What do I look for?
ty,kcopp
Natural gas.
Called TT.
ty,kcopp
Check the refractory. I had kind of the same problem documented here:
http://forum.heatinghelp.com/discussion/159962/prestige-solo-problems#latest
Also, check out your MCBA board to make sure you don't have one with a bad transformer.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
- 109 Chimneys & Flues
- 975 Plumbing
- 387 Solar
- 17 Recall Announcements
