Almost Done
Dan Foley
Member Posts: 1,268
Brian, Poppy, Dragon and Pedja have been working on this project in The Plains VA for the better part of two years. We are hitting the home stretch now. The main house is about 26,000 sq. Ft.
Some interior shots of the main house. Many hours were spent with the architect to make the mechanicals blend in with the architecture.1
The mechanical system is geo based with boiler back up. Six water to water units provide hot/chilled water for the radiant heating and cooling system.
12 packaged geo air units provide 2nd stage cooling, ventilation and de-humidification.
Two 120 gal tanks for DHW are heatied by the boiler. DHW pre-heat off the geo de-superheaters store in two 80 gal tanks.2 -
The 12,000 sq ft guest house is next. It will also have geo based radiant heating and cooling with boiler back up.1
WOW, that is impressive.
2 -
Is her house the same size?DanHolohan said:That's almost as nice as the job you did at Erin's house!
It's a shame you couldn't do an in depth video documentation, like TOH, but more than 10 minutes. This could've been a mini series.
I'm amazed at all the phases-design, bid, install?
Did you design/engineer the job? If not, did the designer/engineer allow your input (if they were smart).There was an error rendering this rich post.
Is this your retirement home, Dan? Nice job (as always)!
That shot of the Viessmann Vitodens: What size 200, BTHB? What is the grey box next to the boiler, just above the horizontal blue raceway - junction box with relays (RIB's) on the perimeter? And what does the silver canister do just to the right of the low loss header - chemical feeder? And is the 3/8" threaded rod the only thing holding the expansion tank in place?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
@ STEVEusaPA
Thanks!
The system was originally designed by a mechanical engineer. As the project evolved and radiant cooling was added, the original design was scrapped and I took over the mechanical design.
When the job is finished, we may shoot video of the entire system if the owner allows.
Here is a link to video shot in the early stages:https://www.youtube.com/watch?v=kTFlcVKbMUo
2 -
Thanks!
The boiler is a Viessmann Vitodens 200 B2HA-112 (113 - 399 input). It powers the two DHW tanks and provides back-up heat for the geo system. It also supplies radiant heat for a six car garage through a heat exchanger.
The grey box is a junction box for heat demands.
The silver canister is a Fernox magnetic dirt separator:
http://www.fernox.us/equipment/filters/tf1+delta+filter
The expansion tank is hanging from a bracket like this:
http://www.dutchtechusa.com/products/flexconsole-standard/
All the weight is supported by the bracket. The threaded rod just holds the alignment in case it gets bumped.0 -
Thanks, Bob !!0
That's really cool! The ultra modern is interesting, how well does the Geo compare to LP as far as cost to operate in your area? Are you using the air handlers to control indoor humidity? What is the setpoint when you know you won't get condensation on the radiant surfaces?
Great project, and beautifully executed as well!
TaylorServing Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
@ Solid_Fuel_Man
The geo was chosen strictly for aesthetics. The architect did not want any visible equipment outside such as condensers, chillers or cooling towers.
The air handlers have two stages of cooling and will provide filtration and de-humidification.
The primary purpose of the radiant cooling is to capture the solar energy from the large expanse of west facing glass that is 14' tall, with no overhang. All of the flooring is stone.
The supply water temperature feeding the radiant cooling will rarely get below 60*F. The control system will calculate dewpoint through slab sensors, air temperature sensors and humidity sensors to keep the surface above dew point at all times.-1 -
Haha! I think my house would fit inside their closet.STEVEusaPA said:
One thing we do have in common is that our mechanical rooms are works of art. Maybe I should host a wine tasting in there too.President
HeatingHelp.com2 -
- 86.8K THE MAIN WALL
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 966 Plumbing
- 385 Solar
- 15.3K Strictly Steam
