Panel Rad placement Question
sibellc
sibellc Member Posts: 13
Hi,
I need advice for panel radiator placement in a kitchen - One location would likely radiate best into the room, but it is 300 btu/h below calculated btu requirements, and much of the output would be convective, as it's 12" tall and quite wide. It's under a tall picture window, so can't get taller. The other location better matches the heat loss calc - 4600 btu/h vs the 4700 btu/h required, but it would appear to be radiating mostly towards the next room. Any thoughts appreciated! Diagram attached.
    hot_rod Member Posts: 26,602
    what about both locations? You want to be sure that you cover the load at design conditions. A bit of an oversize may allow you to run lower supply temperature and outdoor reset controlsy
  • sibellc
    It's going to be installed with a Knight KHN Mod-Con with outdoor reset, buffer tank and TRV on each rad, homerun to a manifold with balancing valves. All rads in the house are sized for 140 AWT after envelope upgrades in the spring - currently being run at 160AWT. I suppose I could do both locations and keep it to around 5000 btu/h. Is there any downside to oversizing more than about 10%? Would you pipe the two in series controlled by one TRV?
    Thanks!
    Sure, two in series sized to the load of the room, two smaller sizes maybe?
    use an H valve with adjustable bypass.