Loop seal?
Paul S_3
Member Posts: 1,291
Is this a loop seal? It looks a little different....i saw this pic on instagram they say theres about 10 of them in the system....maybe at the ends mains....its a one pipe steam system and the bottom pipe is all wet .... I dont see a point for this
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
Hmm, false waterline more likely. Or, as always, could have just been a knucklehead!0
@EzzyT you are correct but @Danny Scully brought up a good point about the false water line with the inverted u sealASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Don't see a need for it unless the return line was above the boiler water line. Seems like they must have had a reason.................??
In the old days they counted every fitting, hard to believe they did this by accident.0 -
A false waterline is a little more complicated and would handle all the wet returns next to the boiler.
Maybe those dry returns are pretty low at that point, and with too high a pressure, the wet return waterline would obscure the main vent, without that configuration.--NBC0 -
Loop sealRetired and loving it.0
Did this allow dimension "A" be less than 14", (18" being preferred)?0
Is there a condensate or boiler-feed pump at the end of that return line?All Steamed Up, Inc.
Consulting0 -
I would think there would be a condensate pump. Otherwise, why trap that main?Retired and loving it.0
there is a condensate reciever
347-692-4777
ASMHVACNYC.COM
That explains it.
The advantage of a loop seal over a trap is that it does not have any moving parts. The disadvantage is that it will not vent air, so you need a main vent to do that. But if a vent fails, it won't let steam into the return and cause banging.All Steamed Up, Inc.
Consulting0
