Loop seal?
Paul S_3
Member Posts: 1,280
Is this a loop seal? It looks a little different....i saw this pic on instagram they say theres about 10 of them in the system....maybe at the ends mains....its a one pipe steam system and the bottom pipe is all wet .... I dont see a point for this
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
Hmm, false waterline more likely. Or, as always, could have just been a knucklehead!0
-
-
@EzzyT you are correct but @Danny Scully brought up a good point about the false water line with the inverted u sealASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Don't see a need for it unless the return line was above the boiler water line. Seems like they must have had a reason.................??
In the old days they counted every fitting, hard to believe they did this by accident.0 -
A false waterline is a little more complicated and would handle all the wet returns next to the boiler.
Maybe those dry returns are pretty low at that point, and with too high a pressure, the wet return waterline would obscure the main vent, without that configuration.--NBC0 -
Loop sealRetired and loving it.0
-
Did this allow dimension "A" be less than 14", (18" being preferred)?0
-
Is there a condensate or boiler-feed pump at the end of that return line?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I would think there would be a condensate pump. Otherwise, why trap that main?Retired and loving it.0
-
-
there is a condensate reciever
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
That explains it.
The advantage of a loop seal over a trap is that it does not have any moving parts. The disadvantage is that it will not vent air, so you need a main vent to do that. But if a vent fails, it won't let steam into the return and cause banging.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements