Melted couplings
HomerJ
HomerJ Member Posts: 1
Suddenly my Beckett AF10 (forced air trailer furnace), has melted 2 couplings within 4 days. What is the cause of the apparent overheated couplings ?
Thanks
  • billtwocase
    billtwocase Member Posts: 2,384
    Negative pressure. Where is the air intake?
    mgdesrochers
  • lchmb
    lchmb Member Posts: 2,997
    make sure nothing happened to the roof jack...
    mgdesrochers
  • mgdesrochers
    mgdesrochers Member Posts: 20
    I'd echo @billtwocase and @Ichmb, something is preventing the unit from properly venting
    EBEBRATT-Ed Member Posts: 20,085
    It may be venting ok while it is running, maybe not. But you have a backdraft, that's about the only thing that will melt a coupling.
    Probably needs cleaning.
    @Ichmb mentioned the roof jack which is an excellent suggestion. The trailer units are usually marginal on draft.
  • billtwocase