low water cut off problem
Buster
Buster Member Posts: 36
We have been called in to try to resolve the issue of the probe type secondary LWCO tripping (right side of unit). The situation happens just before or right after the unit cycles off on pressure. We are aware that the header is not correctly piped and it is getting resolved. Some other piping issues away from the boiler are also getting addressed. The water line does not go below the primary LWCO/feed control when the secondary trips....I have noticed that the equalizer does not get very hot more than about 12" down from the header.
All input would be greatly appreciated!
  • adambnyc
    adambnyc Member Posts: 260
    That LWCO is supposed to be on the boiler. It looks like it's sticking into the side of the Hartford loop. When you get the boiler repiped, get the surgeon to put the LWCO where it's supposed to be.
  • Buster
    LWCO is piped into the return to the boiler below the 'T'. It is a secondary, the primary is piped into the boiler. Why would its position be a problem? The pipe that it is in should always have water in it if the sight glass has water in it and the primary is not tripping.
  • Abracadabra
    I see new piping. Was boiler skimmed?
  • KC_Jones
    KC_Jones Member Posts: 5,883
    What is the height of the secondary compared to the primary? Your wording implies they are at different heights.
    2014 Weil Mclain EG-40
  • Buster
    Secondary is 1.5" lower than the primary which puts it .5" above the bottom sight glass nut.
  • Buster
    Unit did get skimmed. We dont get any evidence of surging either
  • You are going to have surging in that equalizer so it's a terrible place for a LWC. Move it to the boiler and fix the near boiler piping to manufacturers specs and you should be fine.
    New England SteamWorks
    newenglandsteamworks.com
    EBEBRATT-Ed Member Posts: 17,786
    Terrible location for the low water cut off.
    Also, get rid of the gastight tyrapped to the water heater gas pipe.
    That is bad news
  • Buster
    Update, Header has been re-piped and LWCO moved to the boiler. Unit is running much better.
    Thanks for the input!
  • Danny Scully
    Danny Scully Member Posts: 1,462
    Come on @Buster! We're all suckers for pictures :wink:
    RomanGK_26986764589
