how to measure TDS if system already has glycol
Options

chuckjg
Member Posts: 5
Comments
-
http://msdssearch.dow.com/PublishedLiteratureDOWCOM/dh_010e/0901b8038010e417.pdf?filepath=heattrans/pdfs/noreg/180-01286.pdf&fromPage=GetDoc
The table on page 6 shows conductivity. Convert that micro sieman to ppm. Maybe confirm with the brand of glycol you haveBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
thanks for the reply, I am using dowfrost. I don't understand how you convert microsiemen to ppm. I read that they are related, but I don't see a conversion factor.0
-
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks, I guess I had to look a little further. I appreciate the help.0