What happened to the TDS?
Zman
Member Posts: 7,611
I am overseeing the construction/commissioning of a large commercial snowmelt system.
The piping system breakdown by volume is:
40% new Pex-a
35% new steel pipe
25% copper
About half of the copper was piping previously installed and used by the original system.
The design specs did not call for any specific water treatment aside from a thorough flushing of the pipes and a fill with 50% water and 50% polypropylene glycol.
The contractor cleaned the system with a commercial borax/nitrate cleaner and let it run for about a week.
The system was then flushed until the PH and TDS where the same as the local tap water.
The pex tubing was not flushed as contamination was a concern.
The system was then filled with tap water and glycol.
The Tap water had a PH of 7.5 and TDS of 120. Both well within the boiler manufactures spec. The glycol PH and TDS where similar.
The system was fired up and running happily for about a month.
I went back to check the water and it has a PH of 7.1 and a TDS over 500.
Any ideas what happened?
40% new Pex-a
35% new steel pipe
25% copper
Albert Einstein
Albert Einstein
Sometimes runtime will stir up stuff and make a second cleaning needed. Was there enough cleaner added? Maybe a second type would have helped...
Did you see the most recent Coffee w/ Calleffi.?
https://www.youtube.com/watch?v=Wgxaox_2Id8 0 -
I did see that one. With over 10k worth of glycol in the system, the only option appears to be demineralizing.
Albert Einstein0 -
One thing they mentioned at the end of the Webinar if that you will lose the inhibitors.0
Yes, it is a bummer. The only way it could have been avoided would have been to run it super hot for a long period of time.kcopp said:One thing they mentioned at the end of the Webinar if that you will lose the inhibitors.
Wasn't really an option with winter coming."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
The TDS goes up due to the inhibitors in the glycol. So it is usually a good increase
In the Dow engineering handbook they show continuity for various % mixes
I think it is in metric units, you'll need to convert to ppm
Typically new glycol runs 10 or so ph. Could be the blend water had something to do with that decrease?Bob "hot rod" Rohr
Living the hydronic dream0