Can I run the flue vent pipe thru interior wall?

sebobin
sebobin Member Posts: 1
We're remodeling our basement. Existing flue vent pipe goes into chimney about 4' from oil boiler/burner. We want to put a wall between the oil boiler/burner and where the flue vent pipe enters the chimney. We're in CT. From what I can find online, I'd need 18" clearance between vent pipe and wall (combustibles) The existing pipe is single wall sheet metal. I read somewhere that if I use double-walled pipe, the clearance is 9" Can I use fire-rated Sheetrock to reduce the clearance? Are there sleeves that can go over the vent pipe to reduce the clearance. Any other options? Thanks!

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Depends, but drywall is combustible. See if this helps

    There was an error rendering this rich post.

  • ChrisJ
    ChrisJ Member Posts: 16,692
    edited December 2016
    Best thing I can think of is if you used something like is used on wood stoves to pass through a ceiling.

    Might be expensive though, I think you need triple wall pipe for that small area. A B-vent only needs 1" clearance but you cannot use that with oil so I think you may be stuck with a type A vent.




    This is certainly not my area of expertise and I'd recommend contacting the manufacturer of such a product. If it can be used horizontally etc.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • BBros
    BBros Member Posts: 41
    Check with metalbestos type manufacturers. Even the type-A have very small clearances to combustibles, like just a couple inches. They make various flanges to deal with this. I've only ever gone through floors with it, but I don't know why a wall would be different.
  • Jamie Hall
    Jamie Hall Member Posts: 25,996
    Also check with both your homeowner's insurance company and the local AHJ -- fire marshal or building inspector, usually. Whether we like it or not, they sometimes have their own thoughts...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Bob Harper
    Bob Harper Member Posts: 1,109
    You can do this if you use type L vent, which is listed to UL 641 for oil. You'd need a listed 'pass-through'. Enclosing the boiler may violate the makeup air requirements. You'd also need a service switch where you enter that room, a switched service light over the boiler, and a grounded 120vac outlet not to mention a Firomatic valve at the boiler. The chimney would need to be relined if not already done so and include a cleanout. Get a sweep to perform a level II inspection with video scan.