Boiler size
Options
347
Member Posts: 149
Hello All,
Happy late Thanksgiving.
I have a quick question.
Sizing a steam boiler replacement, I came up with 394.5 square feet of EDR. This does not include a missing radiator missing from one room (homeowner said he will not install one, but knows about the future) and the kitchen that has radiant heat. The radiant heat has a external coil that will need to be reconnected the new boiler (gas).
I would like to install a Peerless 63 series but the net rating are either 383 SF or 458 SF.
Which one would be the best fit. I'm thinking a little smaller would be better.
Thanks
Happy late Thanksgiving.
I have a quick question.
Sizing a steam boiler replacement, I came up with 394.5 square feet of EDR. This does not include a missing radiator missing from one room (homeowner said he will not install one, but knows about the future) and the kitchen that has radiant heat. The radiant heat has a external coil that will need to be reconnected the new boiler (gas).
I would like to install a Peerless 63 series but the net rating are either 383 SF or 458 SF.
Which one would be the best fit. I'm thinking a little smaller would be better.
Thanks
0
Comments
-
The 383 should work fine, given the boiler has a 30% additional pick-up factor built in that is not included in the SQ. Ft. of Steam on the rating plate.0
-
I have a second question also. I just looked through the installation manual and Peerless recommends the use of one riser off the boiler (which come with two taps), I'd like to use both, does anyone see a problem with this?0
-
-
Going to do a drop header. Just trying to figure out if I should keep it 3" or come 3" out both taps and reduce to 2" with 3"x 2" 90's and pipe the rest with 2" .
0 -
If the boiler tappings are 3", Do it all with 3", risers and header.0
-
That,s what I was thinking. What do you think about the size?0
-
Best not to reduce Riser tappings out of the boiler and a 3" header should work great.0
-
Thanks0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements