To Insulate Or Not
cheezhd
I recently purchased an early 1900s house with my first steam heat system (1-pipe). I have been getting ready to insulate the uninsulated mains with 1 inch fiberglas, but I recently noticed that the boiler appears significantly oversized. The boiler is 128,000 BTU, but my EDR calculation suggests I need only 56,504 BTU. I'm now worried that insulating could lead to significant short cycling. The main is about 80ft of 2 inch iron, and it has a single Gorton #2 main vent (I believe that's all there is currently room for as the vent only has a 1/4 inch tapping). Is the risk of bad short cycling a serious concern that weighs against insulating or shall I go ahead and insulate?
Any advice is most appreciated!
Are the steam pipes heating an area you use, or, are they directly under an area you want a warm floor in?
If they are, I'd leave them exposed.
If they're in a drafty cold area where you're going to lose a ton of energy I'd probably insulate them.
What boiler do you have?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
It is not that difficult to drill and tap for more venting on the end of the main.
You could also investigate the feasibility of having a 2 stage gas valve installed on your boiler. It would drop down to perhaps 60% of your existing valve. Would take some set up and different control system components.0 -
If you can seal up the area the pipes are in and there is living space above I would leave the mains bare but I would insulate the boiler header.
3PSI gauge0 -
Thanks. The boiler is a Smith GSX 206, and it's in an unfinished basement that does get chilly. The pipes are hung a few feet from the ceiling, so I don't think they're doing all that much to heat the floor above.0
My cellar gets into the low 50's now that my piping is insulated. Before the insulation it was about 7 degrees warmer but I don't spend as much time in the cellar these days so I decided to insulate the pipes a few years ago.
make sure you aren't going to put your water pipes at risk of freezing if that cellar gets too cold.
3PSI gauge1 -
You'd be amazed.cheezhd said:Thanks. The boiler is a Smith GSX 206, and it's in an unfinished basement that does get chilly. The pipes are hung a few feet from the ceiling, so I don't think they're doing all that much to heat the floor above.
You can replace that Gorton #2 with a Barnes and Jones BigMouth and get about 50% more venting even with that 1/4" pipe. That 1/4" pipe will vent about 3.4 Cubic feet per minute. The Gorton 2 will vent 2.2 CFM and a BigMouth will vent 3.6 CFM, (all at 3 ounces of pressure). In this case you'll get 3.3 to 3.4 CFM of venting. You will have to change your 1/4X1/2" coupling with a 1/4X3/4" coupling.1
- 133 Chimneys & Flues
- 172 Indoor-Air Quality