I recently purchased an early 1900s house with my first steam heat system (1-pipe). I have been getting ready to insulate the uninsulated mains with 1 inch fiberglas, but I recently noticed that the boiler appears significantly oversized. The boiler is 128,000 BTU, but my EDR calculation suggests I need only 56,504 BTU. I'm now worried that insulating could lead to significant short cycling. The main is about 80ft of 2 inch iron, and it has a single Gorton #2 main vent (I believe that's all there is currently room for as the vent only has a 1/4 inch tapping). Is the risk of bad short cycling a serious concern that weighs against insulating or shall I go ahead and insulate?
Any advice is most appreciated!
Any advice is most appreciated!
0
Comments
-
Are the steam pipes heating an area you use, or, are they directly under an area you want a warm floor in?
If they are, I'd leave them exposed.
If they're in a drafty cold area where you're going to lose a ton of energy I'd probably insulate them.
What boiler do you have?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
It is not that difficult to drill and tap for more venting on the end of the main.
You could also investigate the feasibility of having a 2 stage gas valve installed on your boiler. It would drop down to perhaps 60% of your existing valve. Would take some set up and different control system components.0 -
If you can seal up the area the pipes are in and there is living space above I would leave the mains bare but I would insulate the boiler header.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thanks. The boiler is a Smith GSX 206, and it's in an unfinished basement that does get chilly. The pipes are hung a few feet from the ceiling, so I don't think they're doing all that much to heat the floor above.0
-
My cellar gets into the low 50's now that my piping is insulated. Before the insulation it was about 7 degrees warmer but I don't spend as much time in the cellar these days so I decided to insulate the pipes a few years ago.
make sure you aren't going to put your water pipes at risk of freezing if that cellar gets too cold.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
You'd be amazed.cheezhd said:Thanks. The boiler is a Smith GSX 206, and it's in an unfinished basement that does get chilly. The pipes are hung a few feet from the ceiling, so I don't think they're doing all that much to heat the floor above.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
You can replace that Gorton #2 with a Barnes and Jones BigMouth and get about 50% more venting even with that 1/4" pipe. That 1/4" pipe will vent about 3.4 Cubic feet per minute. The Gorton 2 will vent 2.2 CFM and a BigMouth will vent 3.6 CFM, (all at 3 ounces of pressure). In this case you'll get 3.3 to 3.4 CFM of venting. You will have to change your 1/4X1/2" coupling with a 1/4X3/4" coupling.1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements