gas meter pipe size
2»
  • Koan
    Koan Member Posts: 450
    @adambnyc , @delta T I assume from the meter plate (picture above) the meter capacity is 415,000 BTU ??
  • Koan
    @adambnyc , @delta T I assume from this name plate the meter capacity is 415,000 BTU??
  • delta T
    delta T Member Posts: 884
    Yes, while technically you are over that load, you are not excessively over and the only thing realistically that would happen would be a slightly higher pressure drop at full load (maybe up to a 1" drop through the meter as opposed to a .5" drop). The tables in the IFGC say that for schedule 40 steel, NG, at less than 2psi static pressrue, you will incur a .5" pressure drop in 10' of 3/4 if you run 360 cu ft. per hour (~360,000) so running everything you have simultaneously will incur a drop higher than .5" but probably still acceptable. I would say worst case scenario you will have no more than a total drop of around 2" between the meter and the section of 3/4" running everything simultaneously. Assuming that the rest of the piping is sized to be less than a .5" drop then you will be fine as long as your static pressure is high enough (7-8" incoming should ensure enough pressure at all times to every appliance. I notice there is no regulator by your meter, do you happen to know what the pressure is coming in to your house? If you have lower pressure, I would change the pipe out and make it right.
  • adambnyc
    adambnyc Member Posts: 260
    Just looked back over the thread and noticed the boiler size. That's a pretty serious boiler. Was curious how many rads you had attached.
    Also, I just wanted to make mention that the 1 1/4 gas line feed may very well have an inner tube of a small diameter. So the actual line could be 1" or even 3/4.
    That was the case in my house. From my understanding, PSEG ran new gas lines about 20 years ago and the practice was 1 1/4 pipe with an inner tube.
    I was lucky enough that when I did my oil to gas conversion that PSEG had to redo my consumption numbers. I knew I was going tankless, so I just told them the additional BTU and they upgraded the line at no cost. Small victory
  • Koan
    @delta T Don't know the feed pressure, would guess 2psig but you are correct there is no regulator. I figured I was just under the load at 405,000 BTU (300,000 boiler, 40,000 HWH, 35,000 dryer, 30,000 cooktop). Even though the inlet is reduced a little I was thinking I'd fix the outlet side but leave the inlet side as is so I don't have to find the outside shut off. At least that way I can just use the existing valve to shut everything off. Next I'll change the outlet diameter to that of the S fitting on the meter ( I assume that is 1-1/4) and use a good 1/4 turn gas ball valve in the outlet pipe and clean up the manifold and piping a bit.
  • Koan
    @adambnyc There are 11 radiators with a surface area of 399 square feet. The boiler is rated for 750 square feet so it is completely oversized. There is a chance it is downfired at lower than the 300,000 BTU but I will clock the meter to check once everything is running again to see what it is actually using.
  • keyote
    keyote Member Posts: 659
    in nyc the utility would own the work before the meter.That not going to be easy to straighten out. I would make certain its really necessary even if it meant not running the dryer on thankgiving while everything else is maxed out it would be worth not messing with, especially since you got to wasting more gas every year with that boiler than it would cost to change the pipe. unless its a castle. my three family 4500 sq ft 100 year home has a heat loss of 52 KBTU and I have a 85 KTBU 10-1 modulating boiler. and that because I have an indirect DHW tank
  • ChrisJ
    ChrisJ Member Posts: 16,864
    edited October 2016
    My 150 year old 1600sqft single family home loses about 72K @ -8F with an indoor temp of 72F and my house is no castle.
    While I realize my loss is quite high for the size building, 52K for 4500sqft seems incredibly low, even for the NYC area?
  • keyote
    I have triple pane windows with krypton, closed cell spray foam insulation,and my design temp in brooklyn is 17 degrees F. Im also although detached its four stories town house so less roof per sf, and a basement is part of that and is 2/3 below grade. and although detached its anly an alley so much less wind and its 3 wye brick behind the spray foam. Im converting to radiant as i renovate i have pics of the boiler KHN 085 I just installed up.
    However I get your point mine is not likely to be a direct comparison,But you're only 72k and hes got a 400k boiler! and be surprised if he need more than a 125k unit and not surprised if he only need a 75k unit. if so for less time and money than replacing those in between gas connections he could pick up a newer smaller unit on craigs list and install it, and save money every month as well.
  • ChrisJ
    I'm not sure in other areas, but in mine the gas company said they'd be more than happy to upgrade me to a larger meter if I want more gas.
    The difference is I have a 1/2" 50 PSI line coming in so they wouldn't need to change that, only the meter.
  • keyote
    I have never heard of gas at that kind of pressure sounds dangerous even with propane they reduce the pressure outside before coming in, here we test at 3 psi for .5 psi service if the pipes been painted they can make you test at 20 psi and that usually means having to repipe because most old gas threaded pipes are not going to hold 20 psi
  • ChrisJ
    edited October 2016
    It's 50 PSI to the regulator at the meter outside. 6" after.
    I had them run the gas in 2011. Last fall I had a guy from the gas co come out to check the pressure and he told me it was 50 PSI to the meter. I was amazed, and his response was "Oh yeah, you'll know if it leaks". It's a 1/2" plastic line with a yellow wire wrapped around it.
    Have a look at the pictures at the link in my signature. There's a picture of the gas meter setup there as well.
    All of the gas piping I ran was tested at 40 PSI. Unions and all. :)
  • SWEI
    SWEI Member Posts: 7,348
    25-75 PSI is pretty standard in modern gas mains.
  • keyote
    I tested mine at 20 anyway but when i bought the house the owner had the gas turned off during contract and couldnt get it passed to turn back on so had to run a new line for old boiler to get through closing.
    Thats an impressive install you did.
    ChrisJ
  • Paul48
    Paul48 Member Posts: 4,469
    I could see a trunk line at that pressure. I'm amazed that a gas company would deliver 50 psi to the door of a residence. I don't doubt it, but that's a little scary.
  • delta T
    Where I'm at it varies between 40 and 60 psi to the reg, then down to 6" into the house. Kind of scary when a regulator goes, I have definitely seen it a few times...at least the utility does usually pay for new gas valves on appliances when the regs do fail.
  • ChrisJ
    What happens? Do the CGVs have an overload that shuts the valve off?
  • Koan
    The more I look at this piping the more I see how poorly it is done. I really don't want to get into anything before the meter, besides, I'm not sure how to shut the gas off outside! The feed to the house is 1-1/2", then goes down to 1" through the main valve then back to 1-1/4 " into the meter.
    For the inlet, I backed into the Spitzglass formula and put it in Excel. 3 90 deg ells for 1" pipe is 7.8 equivalent feet. there is not much pipe so assume 8 feet of 1" pipe. with all things firing at once (397 CFH = 397,000 BTU/hr) that pressure drop is 0.21" wc.
    Not great but nor horrific. Does pressure drop before the meter even matter??
    For the 3/4" pipe out of the meter with the 90 ell that would be about 3.1 equivalent feet. That means at full load I lose 0.33" wc for that section alone. Since these together are over 0.50" wc, I have to hope prior to the meter does not matter.
    Either way, I am thinking I will run the 1-1/4 for the 300MBTU/h boiler right into a 1-1/4 valve then into the meter and then tap off the 1-1/4' for the HWH, Dryer, and cooktop. The only run of any length is the 3/4" cooktop at 30 feet with 3 tees and 4 ells for a total of 50 equivalent feet and even at 35MBTU/h (35CFH) the drop is only 0.04"wc
    BTW Baltimore city requires a 30 psig test.
    looking forward to the feedback!
  • bob_46
    bob_46 Member Posts: 813
    Maybe you are in an area that still has low pressure district regulation where there is not a regulator for each building.
    Charlie from wmass
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,417
    The large supply pipe to the building would be an indicator of that
    cell # 413-841-6726
  • Koan
    I do think we are in such an area. I guess that means sizing the pipe better be right cause there cannot be an increase in pressure!
  • Tim McElwain
    Tim McElwain Member Posts: 4,656
    If I were you I would get in touch with your local gas utility to insure what you are working with. Then do a pipe sizing set up in line with NFPA 54 pipe sizing charts. I can help you with that if you draw up a piping plan showing lengths of pipe and appliance load at the end of each run. As to gas pressure get a manometer and measure pressure after the gas meter. It looks like this is a low pressure piping system from the utility so you should have between 7" W.C. to 10" W.C. (less that 1/2 a pound) after the meter. This should be adequate if the outlet piping is sized correctly. I would suggest using the chart in NFPA 54 which allows a pressure drop of .3" W.C. and no more that another chart which allows .5" W.C.
  • Koan
    Good advice @Tim McElwain . I think I'll leave the inlet side alone, run 1-1/4 to the meter and then branch off wit 3/4 after the Furnace. Earlier in this thread you can see the choke point of a 3/4 pipe and an ell then a tee then up to 1-1/4. Makes no sense. I have the loads listed earlier in the thread as well, the boiler is 300MBTU/H, dryer 22, water heater 40, cook top assuming 35. Longest run is cook top at 50'.the other loads are all no more than 25 ', and the 1-1/4 goes only to the furnace. I calculated the pressure drop and they are a good deal smaller just by running the 1-1/4 right to the meter, then using reducing tees off the 1-1/4 for the smaller loads. I'll try to draw it up. Been using the table you suggested as a guideline.. 0.3 " drop, 2psig or less sch 40 . Got from the IFGC, but I checked with NFPA and it is the same. Thanks for the help!
  • delta T
    @ChrisJ Usually when the reg fails, I see about 1-2 Psi coming into the house, which is still scary, but not 60. I don't know if the regs are just designed that way, but I have never seen it go over that in the house. It does fry gas valves though, they are not lying about the 1/2 psi max....
    ChrisJ
  • Tim McElwain
    Most redundant gas valves (required since 1979) have as the first valve a direct acting solenoid valve which will not open if gas pressure exceeds 1/2 pound (14" W.C.) on older single seat valves excessive pressure will however damage the valve.
    A lot of new setups from utilities have excess flow valves which will shut down if excessive flow due to over pressure or a break in the piping system.
    ChrisJdelta T
  • Koan
    in looking for a 1-1/4 quarter turn valve to mount coming out of the meter, the only ones I can find specifically for gas have a pilot tap I do not need, and they are very expensive. Can I use a normal threaded quarter turn valve?? I have linked to both:
    supplyhouse.com/Apollo-Valves-50GB6A1-1-1-4-Gas-Shut-Off-Ball-Valve-1-4-Tap
    supplyhouse.com/Watts-0555105-LFFBV-3C-1-1-4-Full-Port-Threaded-Ball-Valve-Lead-Free
    so can I use the second one as a shut off on the outlet of the meter? There is no valve there now at all, just one on the inlet side.
  • Tim McElwain
    That is not required as long as there is a shut off before the meter. There should then be shut off within 6 feet of the heating and hot water. All other appliances should have shut offs as close to the appliance as possible.
  • Koan
    @Tim McElwain Thank you sir!!! One less thing to worry about!! Just to be safe I would like to take you up on the offer to review the proposed pipe diagram please. I think it is ok, but I want to make sure I am not screwing up something. I want to make allowances for potential future changes as well. I'll try to diagram the current mess along with proposed changes. Thanks Tim
  • Tim McElwain
    Send it to my e-mail address gastc@cox.net.
    Koan
  • Koan
    thanks Tim!
  • Formerly
    Formerly Member Posts: 79
    just a PSA: spam bots spider through web sites and will add your email if you give it out. next time, spell portions of it (gastc AT cox DOT net) Not a big deal if you use gmail, but with cox, not sure how good their spam filtering is.