Combustion question
drhvac
Member Posts: 190
in Gas Heating
Approximate readings before and after gas pressure was adjusted. What's better?
Before
Gas pressure 3.6
Stack 295
Co2 6.34
O2 9.2
Co 9ppm
After
Gas pressure 4.25
Stack 325
Co2 7.4
O2 8
Co 10ppm
This is an 80% gas furnace. Isn't it a better burn to try and get the Co2 up closer to 7.5 - 8 as long as the co, stack, etc is at exceptable numbers? I was concerned about the gas pressure being to high, but if all the other readings are good, seems fine to me?
Thoughts, thank you.
Before
Gas pressure 3.6
Stack 295
Co2 6.34
O2 9.2
Co 9ppm
After
Gas pressure 4.25
Stack 325
Co2 7.4
O2 8
Co 10ppm
How's that if all the other numbers are good? Stack temp is only 325, and there was a 55 temp rise.0
You did the correct thing. You brought the furnace up to its actual rating versus its factory de-rated design. The orifices are small and raising gas pressure is easier than finding the correct orifices which most manufacturers state in their instructions. I am surprised your O2 only dropped 1.4% with the gas increased 3/4". That equals about a 10% increase in gas. Flue temperature range for that furnace is 302 to 402 degrees so you brought up to where it belonged. To explain LHV and HHV might take to long but natural gas is only 90% sensible heat. So it takes 110 cu ft of gas to have a real 100,000 btu input.0
I would leave the gas valve set for 3.5" as per manufacturer and call it a day.0
@Ironman he definitely is. Fan speed is a big part of the equation. Also you must look to see if it's labled a warm air furnace along with the ratings for temperature rise acrossed the furnace.
If you return temp is 65 and the supply is 120. I see no problems with that at all.0 -
Captainco, the numbers I gave you were estimated, here are the exact numbers after I raised the gas pressure and made the adjustments. I'm always looking to get the o2 and Co2 as close as possible as long as the co, stack temp, etc is right.
Stack 320
Co2 7.34
O2 7.8
Co 9
Co af 14
Draft .0250 -
There are five basic elements of heat transfer:
Temperature
Mass
Line of Sight
Residence Time
Specific Heat Capacity of the Heat Exchanger.
Increasing gas pressure improves the first four. The specific heat capacity is affected by soot or scale.
To adjust a piece of equipment to produce its rated btu output is the right thing to do. Because most heat exchangers are 20,000 btus each and there is no orifice made that delivers 20,000 btus @ 3.5", the only choice is to adjust the gas pressure. The other choice is to return the equipment to the manufacturer and ask for one that is the btus they say it is.
If you bought a 3 Ton A/C unit and it had a 2-1/2 ton compressor in it I don't think you would be happy. But we buy furnaces all the time that are manufactured with smaller orifices than they are rated. Is this a scam or do they think we are to dumb to notice?
- 15.8K Strictly Steam