Erie Valve Wiring

Options
bbilodeau
bbilodeau Member Posts: 2
I'm installing an Energy Kinetics System 2000 and using Erie zone valves. Both leads are black although they connect to blue and yellow wires on the motor. Is there a positive and negative or does it not matter? Thanks.

Comments

  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    edited October 2016
    Options
    Does not matter as the valve is 24 volts ac.

    Taylor
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • hot_rod
    hot_rod Member Posts: 22,142
    Options
    Are there two or four wires coming out of the Erie valve?

    A 24V valve?

    If only two, those are for the motor, no polarity.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • bbilodeau
    bbilodeau Member Posts: 2
    Options
    It is a 24V two wire, so no polarity, thanks!