i have 2 faulty end switches on these wirsbo actuators.....they have new uponor actuators on the same radiant manifold...i cannot seem to locate a replacement for these through supply houses....Any recommendations please Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
I think they are just re-badged Honeywell Sparco actuators, fairly easy to find.
It looks like the white Uponor thermo electrics also work?
Living the hydronic dream1 -
thanks @hot rod .....ill be going with this uponor actuator....
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Confirm with Uponor that the pin stroke matches the older type actuator. If the dimension are not exact the valve could be held partially open all the time, or not open fully if the stroke is shorter. Sometimes a spacer adapter is required to assure that.Bob "hot rod" Rohr
like this? i ordered it tooASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
Yep, if that is the transition ring required to match the old with the new.
Keep an eye on current draw when you start loading up thermoelectric actuators. Most manufacturers now offer low current draw versions. Be patient they take longer to fully actuate or if you are waiting for end switch contact.Bob "hot rod" Rohr
@hot rod .....i never replaced one of these....they just spin off?.....and if i have to purge loop by loop what do i do.....there no individual valves on the return.....thanks Paul SASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
I've not used that brand recently, some of the new actuators can be locked open for purging. Some come locked open and will release after the first power up.
With the actuator removed from the manifold that port is full open. Screw the actuator on, leave it unpowered and that port is closed.
Or get the plastic caps that ship with most manifolds and use it to open or close the various branches for purging. Maybe some were left behind at the jobsite? The plastic cap, when screwed down shuts off that port so you can easily do a loop by loop purge.
With a 4 port manifold, you may have enough fill flow in "fast fill" mode to purge all 4 at once.
The TwisTop actuator that we offer allows you to manually lock open a zone. It also "makes" the end switch when you manually lock it open if you want to start the circ for purging.
You would need to test and see if this actuator would work on that manifold. Threads will match, but maybe not the stroke.
thanks @hot rodASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
- 85.7K THE MAIN WALL
- 51 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities