Heat pump performance
                
                    debrucer                
                
                    Member Posts: 2                
            
                        
            
                    Is it unreasonable for a heat pump to maintain 72 degrees inside when the temperature outside is 95 to 100 degrees?                
                0                
            Comments
- 
            Depending upon sizing. Is 95-100 typical weather there or higher than normal? The general sizing methods say keep the house 75 on the hottest day of a typical summer. Most dealers oversize, some considerably. If 100 is about what you run in the summer, then a "properly" sized A/C in the hottest time of the day could struggle to get 72. If the unit is oversized, like mine, it will do it.1
 - 
            Thanks John
Just for the record,
I live in Florida. The house is a single story, with close to 3000 sf and the unit is 5 ton. It is also has 4 zones. The unit was just installed less than 2 years ago. Even with the 2 sleeping zones set at 78 degrees the other 2 steadily rise in temperature during the afternoon hours to 77 -78 degrees as well regardless of how I set the thermostat.0 - 
            Sizing ac is not a trivial matter, glass plays a very heavy roll in this topic. 75 is the official standard for inside temp. I am in Massachusetts, nowhere near as toasty as FL, but we do get heat waves. Our official design temp is 87, and of course it can hit 100.
Was this a replacement system? Are you sure the installers did their job properly? These systems need the correct amount of refrigerant.
Gary0 - 
            Is the duct work good. Major leakage in the duct system can grossly reduce system operating efficiency.0
 - 
            Do you have good airflow coming out of the vents?0
 - 
            The unit could be bouncing off of high head pressure switch. Actually could be a million reasons for poor performance0
 
Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements
 