Boiler Sizing
SteamGuyDetroit
Member Posts: 1
When removing a customer from district steam, does anyone have an old formula for sizing the boiler when the steam usage is known?
Example, if the worst case usage was January 2014 of 296Mlbs.
If you calculate the total EDR of all the radiators in the customers house/structure, then you can size the boiler based on that number.0
Tell us more about the job- residential? Commercial? What type of heat transmitters in the rooms- or are they all fan-coils?
Is Detroit shutting down its district steam system?All Steamed Up, Inc.
Consulting0 -
Don't forget to add a piping and pickup factor to the total EDR. Multiply the total EDR by 1.33 for insulated pipes or 1.5 for uninsulated pipes and then select the boiler from the D.O.E Heating Capacity rating column in the boiler literature. See pages 73-75 in The Lost Art of Steam Heating by Dan Holohan.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
I would suggest his quote include insulating the mains and any accessible run-outs/returns before I increased the boiler pick-up/piping factor.Don't forget to add a piping and pickup factor to the total EDR. Multiply the total EDR by 1.33 for insulated pipes or 1.5 for uninsulated pipes and then select the boiler from the D.O.E Heating Capacity rating column in the boiler literature. See pages 73-75 in The Lost Art of Steam Heating by Dan Holohan.
What sort of system is this-two-pipe, or one-pipe?
If two-pipe, the pickup factor could be much lower than one-pipe. This assumes generous boiler piping, following the manufacturers requirements at a minimum, assuring dry steam at low ounces of pressure.
Go with gravity, and forget using a condensate pump for best effect.--NBC0 -
If you know the EDR of the installed radiation just select a boiler that has a SqFt of steam rating that is about the same or higher. That SqFt of steam already includes a 33% pickup factor for piping. If the piping is well insulated you can go below the EDR number, if it's all bare steel it should be insulated for good performance.
3PSI gauge0 -
Would this be true if it also had an indirect water heater attached also?0
Generally, yes -- at least in a residential setting.0
- 87K THE MAIN WALL
- 114 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar
