Boiler Sizing
SteamGuyDetroit
Member Posts: 1
When removing a customer from district steam, does anyone have an old formula for sizing the boiler when the steam usage is known?
Example, if the worst case usage was January 2014 of 296Mlbs.
Example, if the worst case usage was January 2014 of 296Mlbs.
0
Comments
-
If you calculate the total EDR of all the radiators in the customers house/structure, then you can size the boiler based on that number.0
-
Tell us more about the job- residential? Commercial? What type of heat transmitters in the rooms- or are they all fan-coils?
Is Detroit shutting down its district steam system?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Don't forget to add a piping and pickup factor to the total EDR. Multiply the total EDR by 1.33 for insulated pipes or 1.5 for uninsulated pipes and then select the boiler from the D.O.E Heating Capacity rating column in the boiler literature. See pages 73-75 in The Lost Art of Steam Heating by Dan Holohan.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I would suggest his quote include insulating the mains and any accessible run-outs/returns before I increased the boiler pick-up/piping factor.Don't forget to add a piping and pickup factor to the total EDR. Multiply the total EDR by 1.33 for insulated pipes or 1.5 for uninsulated pipes and then select the boiler from the D.O.E Heating Capacity rating column in the boiler literature. See pages 73-75 in The Lost Art of Steam Heating by Dan Holohan.
0 -
What sort of system is this-two-pipe, or one-pipe?
If two-pipe, the pickup factor could be much lower than one-pipe. This assumes generous boiler piping, following the manufacturers requirements at a minimum, assuring dry steam at low ounces of pressure.
Go with gravity, and forget using a condensate pump for best effect.--NBC0 -
If you know the EDR of the installed radiation just select a boiler that has a SqFt of steam rating that is about the same or higher. That SqFt of steam already includes a 33% pickup factor for piping. If the piping is well insulated you can go below the EDR number, if it's all bare steel it should be insulated for good performance.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Would this be true if it also had an indirect water heater attached also?0
-
Generally, yes -- at least in a residential setting.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements