Low loss header - boiler side - pump away? (or to the boiler?)

Options
Chuck_17
Chuck_17 Member Posts: 143
Typically for a primary secondary boiler connection, the boiler (secondary) pump would pump "to" the boiler.
But what about if you are using a packaged low loss header?
The Lochinvar boiler install manual shows the boiler pump pumping "to" the boiler.
The B&G low loss header shows the boiler pump pumping "away" from the boiler (to the header). (Actually it shows the boiler pump pumping away for the example secondary loop also.)

The system pump would pump "away" either way (not in question).
I'm inclined to go with the boiler detail. What do you think?

Comments

  • Paul S_3
    Paul S_3 Member Posts: 1,261
    edited June 2016
    Options

    the lochnivar boilers do not have a substantial pressure drop across there heat exchangers... i believe the wh and khns are very low .....the reason most modcon boilers show the boiler pump on the return is because of that substantial pressure drop on that specific boiler ..... best way is pump away from "the point of no pressure change" using a low loss header i would pump toward the boiler on the the boiler side of the header....( LLH is the point of no pressure change for the boiler pump) install the system pump on the supply of the LLH , pumping away from the expansion tank....Caleffi idronics has nice diagrams for this.
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    Zman
  • hot_rod
    hot_rod Member Posts: 22,139
    Options
    A properly proportioned separator presents very little pressure drop in the system. Ideally a 3-1 ratio, pipe size to barrel dimension.

    As such, expansion tank connection near any of the 4 ports establishes the PONPC through the vessel.

    On caution is to avoid the expansion directly below the sep to prevent any dirt removed from settling on the diaphragm in the expansion tank. If you use the bottom connection install a tee and pipe the expansion tank off the branch.






    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Paul S_3Roohollah
  • SWEI
    SWEI Member Posts: 7,356
    Options
    Which Lochinvar boiler specifically? Some of their older designs use high head loss heat exchangers and those are quite different with respect to pumping requirements.
  • Firecontrol933
    Firecontrol933 Member Posts: 73
    Options
    Just thinking out loud, but on the low mass mod cons, if you pump towards the boiler you keep the water at the HE at the highest pressure in the loop/system. This "might" help in certain conditions where the fluid against the outer wall of the HE might want to flash.

    It's more of a worse case scenario thought, but even the best system design and installation someday will suffer from some form of issue and why not give it the best chance of the least amount of trouble when that time comes.
    Gordy
  • SWEI
    SWEI Member Posts: 7,356
    Options
    Higher pressure in the boiler can work against you in a tall building.

    Pumping on the return does lower operating temps for the circulator.
    Gordy
  • hot_rod
    hot_rod Member Posts: 22,139
    Options

    Just thinking out loud, but on the low mass mod cons, if you pump towards the boiler you keep the water at the HE at the highest pressure in the loop/system. This "might" help in certain conditions where the fluid against the outer wall of the HE might want to flash.

    It's more of a worse case scenario thought, but even the best system design and installation someday will suffer from some form of issue and why not give it the best chance of the least amount of trouble when that time comes.

    More so high pressure drop type boiler HXers. Copper tube boilers are considered low mass, low water content, but have large short tubes, not as much pressure drop as some coil type mod cons.

    There are some brands of mod cons that have pressure switches on the boiler for low water conditions, you defiantly want to pump into those.

    Really no harm in pumping into any boiler, as long as the expansion tank is located upstream of the circ pump.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream