Heat loss by usage?
13
  • Brewbeer
    Brewbeer Member Posts: 616
    edited April 2016
    Heat loss calc for my house came in at about 32K, usage estimate is about 24K at a design of 0F. SWT of 130 at design.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
    njtommy
  • Gordy
    Gordy Member Posts: 9,546
    Key point is having the emitter to absorb the btus. As ME pointed out in his last post. Over emitterization plays a very crucial role.
    njtommy
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    edited April 2016
    "The poor slobs who use the Manual J approach".
    Really???
    I think the contractors who you just insulted are the ones who are head and shoulders above the rest.
    Garbage in. Garbage out.
    Steve Minnich
    Mark Eatherton
  • Leon82
    Leon82 Member Posts: 684
    I have a feeling he was being mildly sarcastic, as I'm sure ME put extra emission purposely.
  • Rich_49
    Rich_49 Member Posts: 2,781
    I won't speak for others but I for one am not offended nor insulted by Hatts comment . We are forced to perform Manual J by most AHJ s and codes .
    Here is the problem . Not many understand Equivalent Full Load Hours . While some are all looking at fuel usage they do not take into consideration the house coasting through higher temp days leveraging the heated mass , stretches where you may have record cold and your customer is perceptually freezing his **** off , have fun explaining the science to that cold **** .
    Since , as Stephen said , We are head and shoulders above the rest . You should not size a boiler by gas usage since these hills and valleys DO EXIST . I might add that if you take pride in what you do and design , restore , repair , install heating systems you should never get calls from your clients that they are cold , EVER . If yoiu are doing your job the best way possible you should be measuring room by room anyway to determine where your temps and such should be anyway .
    Imagine the poor **** that read this and follow the USAGE Guy's advice . They'll use the winter of 15-16 and in 16-17 ,
    17-18 their customers will not be pleased . Fuel usage can go very wrong , a room by room and knowledge rarely will .
    732-751-1560
    Rich McGrath 732-581-3833
    Mark EathertonnjtommyGordy4Johnpipe
  • Rich_49
    Extra emitter is always a good idea since it will allow for lower water temps for more of the year but still have capability during those peaks .
    732-751-1560
    njtommyGordy
  • Steve Minnich
    I say put in all the emitters you can... or your wife will allow.
    I've been doing quite a bit of work at churches that have peak use once, maybe twice, a week. Usage won't do me any good there. But a room by room loss will insure I never get a called out on my day of rest.
    Steve Minnich
    Rich_49Mark Eathertonnjtommy4Johnpipe
  • ChrisJ
    ChrisJ Member Posts: 16,873
    I think it's a skill and an art like anything else.
    2015-2016 was a mild winter in our area, you'd have to be a fool to use that to size a heating system.
    Now using 2014-2015 on the other hand should yield very good results.
  • SWEI
    SWEI Member Posts: 7,348
    Very similar experiences here -- Rich and Mark both described it well. Ganged mod/cons on commercial projects (and huge houses) ROCK. When properly sized to the heat loss, one third to one half of the heating plant is all that will ever fire, except perhaps during peak DHW demand periods.
    In the electrical/electronics world we use the term crest factor, and it represents the peak to average ratio of a signal. Most nights, OAT drops noticeably right around sunrise, often by 5-7°F. Very, very few buildings can't carry a two hour dip. Masonry buildings (even when leaky and quite old) can take DAYS to heat up or cool down significantly. Building mass is completely missing from both the Manual J and ASHRAE/IBR heat loss methodologies. There are sophisticated energy modeling packages that do consider mass, but they require detailed 3D modeling of the structure and envelope that would be cost prohibitive to do for most existing structures.
    Rich_49Mark EathertonGordy4Johnpipe
  • njtommy
    njtommy Member Posts: 1,105
    You guys bring up a lot great points.
    I've never seen an undersized boiler only over sized. I will completely admit I've done it my self. Not on purpose, but mainly lack of knowledge and understanding.
    Robert O'Brien4Johnpipe
  • ChrisJ
    Yeah.......99% of steamers installed.
    njtommy
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,577
    You just can't resist the ad hominem attacks! USAGE Guy is an ad hominem attack,as it would be if I were to refer to you as "HTP shill guy" I've asked you nicely to refrain from this,yet you persist? I also suggest you brush up on what is a PM and what isn't.
  • Rich_49
    I was in no way singling you out Robert as opposed to addressing the differences between one method as opposed to another . Several others have advocated for usage also , what would make you think I was specifically talking to Robert ? You are not that important , simmer down and quit pissing in my Cheerios . Have no doubt comrade , if I want to address you it will read @Robert O'Brien
    I don't take much offense to HTP Shill guy either , I have the sense to use quality equipment from a manufacturer that gets it and supports their product with integrity .
    Have a good day BOB !
    732-751-1560
  • Robert O'Brien
    "Since , as Stephen said , We are head and shoulders above the rest ."
    Modesty is your middle name! Your sense of self importance, arrogance and rudeness are as endless as your humility is non existent! And I still have the taste of Munchkin in my mouth! Good day!!
  • Rich_49
    edited April 2016
    Hmmm , you have no idea how wrong you are .
    Learn the words you are using also , Ad hominem would entail an attack on your person or character , neither of which I have ever done . Can you say the same , Mr . humility , arrogance , self importance ? If Giant Rectum inflamed you so you really are flower .
    732-751-1560
  • gennady
    gennady Member Posts: 840
    edited April 2016
    I guess most times boiler is working in steady state, house is warm and set. Heat loss by fuel consumption reflects it. Now here is scenario. At design temperature boiler fails at night. Plumber comes in the morning, house starts to freeze up. Plumber fixes the problem, boiler starts.
    -It is yearly morning, still dark ( no solar gains)
    -most of electrical appliances off,
    -no lighting ( no internal gains).
    -strong wind ( high infiltrations)
    Will boiler be able to pull this house off if boiler is sized based on steady state fuel consumption?
    Just asking. Always eager to learn.
    Rich_49
  • Gordy
    Radiation density plays a key role in this.
  • gennady
    edited April 2016
    Or another scenario. 2 identical houses, one next to another. One has properly sized boiler, running on outdoor reset, TRVs. another one has oversized boiler, short cycling, unbalanced system, half of the house is cold, another half has windows wide open. You get the picture. Both need new boiler. Sizing is by fuel usage. Would they get same size boiler?
    SWEI
  • ChrisJ
    You're asking for the boiler to pull off a 40°F climb on the design day with high winds?
    I might suggest that any boiler sized exactly to the heatloss via Manual J or via the heatloss via fuel consumption will fail at that endeavor.
    Once you're at design, there is precious little margin for winds in most localities. There is certainly no margin to enable a large climb in any reasonable amount of time. The first 20°F will happen relatively quickly.............the second 20°F is going to take forever if it happens at all.
    But, like most design days...............they come and they go. Patience is a virtue.
    I don't know.
    My "undersized" steamer could pull off a 40 degree climb on design day with high winds no problem. In fact, I'd bet it could do it 20 degrees below design day.
  • Robert O'Brien
    edited April 2016
    Conversely, I ask if you would do a heat loss on one of these homes after already doing them on quite a few others? FYI, they are oil, no gas available. 900 square feet as seen in this pic although they have been added on to in the ensuing 65 years but based on lot size, they can't get very big! And there are 17,000 in just this development.
  • jonny88
    jonny88 Member Posts: 1,139
    edited April 2016
    Off topic a bit but I was just on the phone with a heating guy I know.Currently he has 22 Munchkins at 14yrs old and actually put one in his g/f house 7yrs ago.Also 8 Munchkins in Bklyn 7yrs old still running smooth.Install and service is the key.Brought it up as Munchkins were mentioned earlier in the thread
    4Johnpipe
  • ChrisJ
    When we are speaking of "undersized" on a hot water system, we refer to the heatloss as compared to the output of the boiler.
    When you are speaking of "undersized" on a steam system, you refer to the standard pickup factor (33%) versus your actual pickup factor and are unconcerned with the heatloss.
    Yes,
    That's why I said it, because we really should be concerned about heatloss with steam. It actually does matter.
    But that's another argument, I'm just hoping Fred won't see it here. :)
    Hatterasguy
  • Robert O'Brien
    Is this a trick question? :)
    Just as much as the question I was responding to!
  • Robert O'Brien
    And she's still sleeping with him? :)
  • Paul48
    Paul48 Member Posts: 4,469
    There's so many things to consider. I don't think there's anything wrong with doing a fuel usage. But, it's not a good idea to use it alone. Use it along with more conventional calculations, and if it doesn't match you need to find out why. Thermal mass, layout of the home, number of occupants, insulation, air infiltration, habits, and expectations all play a part.
    If you don't take the time, you WILL let some of your customers down. We've seen it here a thousand times.......a contractor installs a mod/con to replace a bang-bang oil-fired boiler, and the customer continues doing what he/she has always done...turn the temperature back 20* at night. The heating professional failed. There are certainly no one-size fits all boilers, of any kind.
    Rich_49
  • Robert O'Brien
    Just here today, one of the 17k Levitt houses. They want the quietest boiler they can get since this in the kitchen. Going to remotely locate an indirect. The quietest boiler that fits is a Firebird condensing oil boiler. Comes in 90k or 120k. Do I need a heat loss to tell me which one to choose? If the heat loss is 25 or 35 or 55 or 65 does it matter? Paraphrasing Hillary there!
  • Robert O'Brien
    Unless they make smaller boilers! The DHW issues can be overcome with a bigger tank and a mixing valve
  • jonny88
    They really are a tough setup.Had a customer recently who wanted his boiler removed from kitchen etc but the price was not in his budget.Gotta see to believe.
  • ChrisJ
    That's oil fired?
    How do you service that!?!?
  • jonny88
    Chrisj they are usually hung in a closet.When they puffback you get some mess.Never enough combustion air etc but all to typical in these homes that were designed at that time .Your joking about servicing right.This is Long Island.Oil companies change filter and nozzle and call it a day.
  • ChrisJ
    The guy I hired back in 2011 didn't even do that much.
    That's what triggered me doing all of my own work.
    jonny88
  • Paul48
    I think if I owned one of those houses, my first "addition" would be a boiler room. Were these built for returning GI's from Korea? I wonder if they were originally electric heat.
  • Robert O'Brien
    WW2. They were radiant, copper tubing directly buried in slab. They have almost all been replaced by baseboard.
  • Rich_49
    732-751-1560
  • Robert O'Brien
    Rich said:
    You're like a dog with a bone, just can't let go! In defending yourself against assertions that you engage in ad hominem attacks, you engage in yet more ad hominem arguments as if that bolsters your position!
  • Rich_49
    edited April 2016
    http://literarydevices.net/ad-hominem/
    Abusive ad hominem usually involves attacking the traits of an opponent as a means to invalidate their argument(s). Equating someone's character with the soundness of their argument is a logical fallacy.
    Ad hominem abuse is not to be confused with slander or libel, which employ falsehoods and are not necessarily leveled to undermine otherwise sound stands with character attacks.
    732-751-1560
  • Robert O'Brien
    Rich said:
    Again you confirm my allegations, your comments are the very definition of ad hominem and then you graciously post affirmation! :)
  • Rich_49
    Robert , this will be my last comment on this issue . I posted the very definition of Ad hominem so anyone who may not know the meaning could see . Please post where I made a personal attack on you or you character on any forum as opposed to enter into a debate with you on the basis of the subject matter at hand .
    You sir , attacked my character traits as you see them which I might add could not be farther from the truth . This in no way negated the validity of the points I made in disagreement with HLCs vs Gas usage .
    You even stated in the piece you published in Mechanical Hub that you were gonna hear it from many . Guess you really were not as ready to hear it as you thought . The comment you made which precipitated this portion of the storm is based on you seeing something that I wrote Hatteras which I thought was private which referred to you using an unflattering term , big deal . You should have kept it offline as I had intended . You CHOSE to attack my character and insult me in the way of pointing to my lack of understanding of the internet and PMs .
    Good thing I am a heating / cooling guy and do not perform IT services .
    Maybe you should read all those definitions again and try to comprehend what they actually mean . Take a breath , calm down and be reasonable .
    Question , what is one of the first questions we ( includes you) ask folks looking for help whom have had a malfunctioning system installed ? Jeopardy music here .
    732-751-1560
  • Robert O'Brien
    Since you asked. These are a few examples of ad hominem arguments. Pretty simple concept really!
    Rich →
    Don't wanna inflame the giant rectum but , He can do his boiler sizing that way but after he does that if he has any inkling to provide a quality product to the end user he will still have to do the room by room and a radiation survey to figure out a reset curve and what temps he can use in his system . So , how much time did this **** save by using the quick and dirty method ? None , unless he has no desire to give the great product .
    Rich July 2015
    What is lost on you Robert is that you believe you are intelligent