hePEX Primary Piping
johntrhodes81
Member Posts: 44
Is piping the primary connections to manifolds, expansion tank, etc out of hePEX a bad idea? As long as there is 18" of copper or metal tube from the boiler?
Thanks,
John
Thanks,
John
0
Comments
-
Not a problem as long as everything is sized and supported properly. Getting tee branches and short runs of PEX to stay level and plumb can be a bit of a challenge.0
-
what temperatures would you be running?
I'm wondering about long term effects of non or less that 100% oxygen barrier tube in high temperature hydronics. Are any of the fusion well PP pipes O2 barriered?
I don't recall many sludge and corrossion issues with boilers, pumps and components until we introduced plastics into the installations?
Guess we will know in 5-10 years like the PB and early rubber tube installations. Are we tempting fate?
I think copper and steel are still the best near boiler piping products. Maybe I'm just getting old )Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
the higher the temperature the more oxygen can pass into the pex, as HR said less than 100% is something, I think it depends on the amount of Ferris metals that can take the "hit" to rid the system of oxygen. Take a mod-con with a stainless HX and a bunch or radiant pex, with an iron circulator and a steel expansion tank there is little else to oxidize and I think we will be seeing those systems eat through the thin expansion tanks in the next ten years. A far cry from CI radiators and boilers piped with 100% closed copper pipe.
SFMServing Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I heard manifolds and assumed PEX downstream. If there's a CI boiler and a mixing valve, hard pipe to the mixing valve.0
-
Mod-con boiler -> Manifolds -> Pex-AL-Pex -> CI Radiators.
SWT between 120 (60 outdoor) and 180 (0 outdoor).
John0 -
Temps seem high to me, most especially at the low end. How were they determined?0
-
I just had to make the same decision- pex or metal for near boiler piping on my new mod/con system.
Decided to go with copper/black pipe up to the manifold after the CH pump- then OB PEX A to the zone valves and out to my existing 3/4" copper baseboard lines.
For the return I'm using OB PEX A from existing 3/4" copper baseboard right up to the return manifold and copper from the manifold to the boiler.
For the indirect DHW heater- all copper to/from the DHW circulator/boiler, but non-OB PEX B for the DHW to house domestic water lines.
It's tempting to use PEX for closer to boiler connections- especially when a two dollar PEX connector replaces a twenty dollar brass union. But, I like the idea of being able to stabilize the circulators, Spirovent, expansion tank, etc... to kindorf and know it's not moving vs. less stable mounting going mostly PEX.0 -
-
...and be sure to flush/purge thoroughly before the new boiler and circ are installed. We use a 20µ cartridge filter on the return line to the purge cart and you wouldn't believe the crud that comes out.0
-
I have done it a time or two... Although I will prob not do it again now that I have a propress tool. I did this install just before Christmas a few years bac and was pressed for time as there was no heat or hot water in the home.
No issues what so ever... The system was cleaned and treated w/ Fernox1 -
House is a mix of Cast iron rads and CIBB .; Heat loss performed , room by room . House has some issues and the temps stated to be required were determined by me based on the parameters given me by John . Made some recommendations , they were listened to but not agreed to for various reasons . For the system to work and John and his family to be comfortable the curve is as stated above . Does that answer how the temps were arrived at ? Good lookin out though Kurt . Temps will be able to come down when further work is completed on the envelope .
John , could you please clarify where it is that you want to use HePex ?
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
I'm taking notes on the circulator to hot water tank mounting in your 2nd photo... is that kosher?kcopp said:I have done it a time or two... Although I will prob not do it again now that I have a propress tool. I did this install just before Christmas a few years bac and was pressed for time as there was no heat or hot water in the home.
No issues what so ever... The system was cleaned and treated w/ Fernox
That would save me some work on my install...
0 -
I was thinking about using HePEX between the manifolds and the boiler, but decided to scratch that and stick with copper. Rich has been very helpful, I really appreciate it. Yes the envelope needs work. Uninsulated Concrete block exterior walls loose a lot of BTU's fortunately the house has alot of radiator capacity.
John0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 926 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements