Boiler size
daileyhome
Member Posts: 3
in Gas Heating
I am replacing boiler in 50 year old classic 2 story colonial home suburban Philadelphia. baseboard. total square ft 3200. old boiler installed 1981 is 166K BTU. My heat loss calculations are coming up with about 90K. this is consistent with my reading that most homes have over sized boilers but I'm hesitant to accept my calculation. Is 90K in the ballpark for my house as described?
How did you calculate it? The slant fin app can be 15 to 20 percent over the actual.0
We replaced a boiler a couple of months ago with about the same square footage and that heatloss came out to be 63,000 BTU's and that was using the slant/fin app.0
28 BTUs per square foot. Entirely possible with 2x4 walls and single pane aluminum sliders. Slab on grade?0
How many feet of baseboard?0
240 ft of baseboard. Craw space. I caclculated using instructions on Weil McLain site and then a spreadsheet model from another results were close.0
You certainly are in the ballpark. Perhaps a little high.daileyhome said:I am replacing boiler in 50 year old classic 2 story colonial home suburban Philadelphia. baseboard. total square ft 3200. old boiler installed 1981 is 166K BTU. My heat loss calculations are coming up with about 90K. this is consistent with my reading that most homes have over sized boilers but I'm hesitant to accept my calculation. Is 90K in the ballpark for my house as described?
It is great that you have so many feet of radiator.
You only need to get 375 BTU/ft out of the baseboards which means you only have to run about 150 degree water on the coldest day.
A Mod/com boiler with outdoor reset would be ideal for you."If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
thanks much for advice and recommendation. i'm thinking simple old fashion cast iron. avoid extra cost and complex maintenance and repairs. initially considering Weil Mclain CGa 7 based on old boiler but calculations are telling me go down to as low as CGa 5. Appreciate any further thoughts and comments.0
Outdoor reset will make a big difference in both comfort and efficiency. If it were my job, and you insisted on a CI boiler, and assuming the heat loss figure was actually correct, I'd spec a CGa-4 with a 4-way Taco iSeries-R valve. It's quite probable the heat loss is less than that, or could easily be made so with some simple envelope upgrades. CGa-3 then.1
All Mod Cons do not require complex annual maintenance and don't cost all that much more . This was made for homes just like yours . Later when you need a water heater also you can fit a 40 plate heat exchanger and one circ and be done .
http://www.htproducts.com/pioneer.htmlYou didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38330
