CH inlet filter
MSR
Member Posts: 9
What is causing my inlet filter to blow out the bottom of my wall mount combi boiler? I ran the system for five days then it blew out. Am I running the pump speed too fast? Should I look at check valves/ remove? Not sure what I am doing wrong.
Whats a ch inlet filter and combi boiler. Can you post a pic?
Im interested, but sorry not much help. Spose i'll learn something cool here.0 -
Are you talking about the wye strainer?....do u have pics of the actual near boiler piping ?ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
It's number 53 on the parts list and the green thing above (E) in the bottom view picture.0
Please post a picture of the ACTUAL INSTALLATION . Include the Westinghouse unit . We need to see what you or your installer did , not what it is supposed to look like in the manuals or on the internet .
Have you called Tech support ? They probably would have a quick answer for you .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38330 -
In what way are you using this unit ? Are you by chance using it for space heating only without the DHW being hooked up ? Where did you purchase this unit and the separate module that it is attached to ?You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
I'm using it for domestic and floor heating. The tech support it has to do with a check valve in a pump but no concrete answer as how to fix it.0
I purchased the whole setup at menards.0
Is it clipped in properly with part 540
Yes, it broke the filter and I had to get a new one.0
I cannot see a pressure reducing valve / backflow prevention device in any of these pictures . Do you have one installed ?
What is the system pressure and how did you purge this arrangement ?
http://www.htproducts.com/literature/lp-537.pdf
Where do the tees on the system supply and return go to ? Could you take another couple pictures from straight in front of the unit showing everything from the floor to the ceiling without any ladders , buckets or the like blocking anything from view ?You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
The tee goes to another manifold with 4 loops and the other tee is the return from that manifold. I have 8 loops total. Pressure for the floor heat was set to 18lbs and the boiler pressure ran about 12. I purged each loop separately until all air was out of that loop. I have a fill and exit point on my panel. That is what I hooked up to to fill and purge. I do not to my knowledge have any back flow prevention device unless that is what the check valves in the pumps do. I have three pressure relief valves, one on the panel, one on the CH supply and one on the DHW supply.0
It is hard to get a full picture because my mechanical room is only 4, wide and I still have my old water heater in it.0
QA pressure relief valve is not a pressure reducing valve . REQUIRED .
Do you have anything that looks like any of these ?
http://www.taco-hvac.com/products/hydronic_accessories/pressure_valves/boilerfeed_backflow/index.html
http://www.taco-hvac.com/products/hydronic_accessories/pressure_valves/cartridge_style_pressure_reducing_valve/index.html
https://search.yahoo.com/yhs/search?p=caleffi+boiler+pressure+reducing+valve&ei=UTF-8&hspart=mozilla&hsimp=yhs-004
ANYTHING like that ?You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Near the expansion tankASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
MSR
Just look at the illustrations in the document I attached . It is published by the manufacturer of your unit .
In the future when you build and install an IED it may be wise to pay attention to the explosive manufacturers requirements and worry less about the fuse .You didn't get what you didn't pay for and it will never be what you thought it would .
732-751-1560
Rich McGrath 732-581-38332
- 121 Chimneys & Flues
- 15.8K Strictly Steam