steam traps
Options
wbjeff
Member Posts: 5
Hi, we are replacing a 100,000 btu steam coil in a duct system. previous contractor had installed a 3/4" float type steam trap on a single pipe steam system with wet returns. Do we need to reuse the steam trap
thanks
thanks
0
Comments
-
On a single pipe system with the outlet of the coil discharging to a wet return, with NO condensate receiver, but rather a gravity return to boiler, there should be NO trap on the outlet of the heater. However, the outlet should have a vent installed, such as a Hoffman 74. It should be configured so that it is even with the top of the coil.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Here is a picture of it. Shows a unit heater, but a coil would be piped the same.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
3/4" sounds large for fractional gpm.
Unit heater manufacturers state that two pipe is required. But I believe that I've seen them used with one pipe. Heater is above pipe and both heater connections are used. I don't think that trap is called for. Generally boiler feed is de-aerated.
The fan controls heater output.0 -
Everone, thanks for the input...jeff0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements