LWCO
vinceM
Member Posts: 81
A lot of old boilers were installed without LWCO's, they can add one off the lower gauge glass fitting.
3PSI gauge0 -
Bob, so am I using the gauge glass to monitor the boiler water level??
I'm always in the basement around the boiler. I have a manual water feed that I was shown to use if I see the water in the gauge glass below the recommended level. Does that substitute the LWCO?0 -
HA! Not very reassuring. Would I be better advised to have a LWCO with auto feed installed0
You'd be well advised to have a LWCO installed. The auto feed is good but as long as the LWCO works, it will shut the boiler down if there is a leak. Many prefer the auto feed, many others, myself included, just check the water level periodically.0
I agree with Fred, the LWCO should be installed to shut the boiler off if the water level ever drops to low. If your down the cellar several times a week you don't need the auto feeder so you'll have to add water if the water level drops over time.
3PSI gauge0 -
Ok. Thanks to all.0
Check inside the jacket in front of boiler. Alternatively, turn off boiler. Drain completely. Turn back on. Boiler won't go on if there is a working LWCO. Obviously, if boiler does go on, shut off ASAP.0
Ha, rickhansell beat me to it, good call !
I was wondering what that device below the switch box was.
Good eye. Didn't spot that. As stated, you can test if it's functioning. Not a bad idea to get a MM 67 as a backup.0
Rick, and others thank you. In fact, after my last post I went down to the boiler late that night and poked around again. There it was!!! Under the switch.I didn't have time to post again.
I looked up the brand, McDonnell 369 float type and yes, no valve or drain present. Seems odd that this type of LWCO isn't designed to be cleaned out or is it??0 -
No need to flush anything because this type sits directly inside the boiler thru a 2.5" boiler tapping.0
Abracadabra, I'm a novice in the subject, please elaborate on your comment.
As Rick stated above it's probably, "Full of mud...." Others have recommended adding a back up that has a flush valve.
Thanks.0 -
Not sure what else to elaborate on. There is no external chamber for mud to accumulate. The float sits inside the boiler casting. Any mud would drop to the bottom of the boiler about 3 feet below.0
OK. So this particular type of LWCO doesn't need to be cleaned. It's "self cleaning??"
If I envision the inside of this 40 year old boiler and the sediment or what have you, is falling to the bottom over these years, would I be safe to conclude: #1- that there is likely a significant amount of debris that has accumulated,#2- this debris needs to be cleaned out.0 -
The key is to drain water out of the boiler and see if the LWCO shuts the boiler down when it gets low enough. Do this when the boiler is cold or just warm and don't run it for any length of time at very low water levels. That LWCO should be removed occasionally to be cleaned.
How dirty is the water that comes out of the boiler drain?
3PSI gauge0 -
Bob, thank you. Understood.
I will have the boiler serviced very soon. I'll be sure to be present.
Since the MM 369 and MM67 are completely different in design and how they are connected to the boiler why is one chosen over the other. I would think a mechanism that doesn't have to be regularly maintained would be preferable???
I'm just trying to understand why they did what they did when my boiler was setup.
Thanks0 -
It may just be what was supplied with the boiler. One would work as well as the other but the 369 is not prone to fouling like the 67 is. A lot of boilers don;t have a 2-1/2" side opening for the 369 so the 67 becomes the default for a water level switch Or a probe type LWCO is used instead.
3PSI gauge0 -
Thank you Bob0
- 15.8K Strictly Steam