Primary Secondary with Reversed Secondary Flow
Kirchof1
Member Posts: 4
in Gas Heating
I recently purchased a house and have been working on improving the efficiency of the hydronic heat system. It's a Munchkin 80M with 2 zones controlled by zone valves and a primary secondary piping configuration. The kicker is that the secondary flow is backwards. Both primary pump and secondary pumps are Grundfos UPS15-58. Based on a heat loss calc and the head loss of the secondary and primary I knew which setting I wanted to run each pump at until I realized that the secondary flow was reversed. I'm wondering what the implications of this are. It's not really a primary secondary system because the secondary return must mix with the boiler supply and flow through the common pipe. Is there a reason that the piping would be installed this way? It seems like the worst strategy for condensation. Any insight would be greatly appreciated. Thanks everyone. Chad
Pics?0
The primary pump is pumping into the return side of the boiler and the secondary is pumping away from the expansion tank, toward the zone valves and out to the house.0
Dont' see a pressure differential by-pass...
You are still piped primary secondary in your pics. The 2 closely spaced tees dictate that..There was an error rendering this rich post.
Gordy said:
Hmmm unless my eyes are crossed I think the piping to the closely spaced ts are reversed. The return from system is headed for the supply on the primary.
Bingo!. Nice catch Gordy they are backwards.Gordy said:Hmmm unless my eyes are crossed I think the piping to the closely spaced ts are reversed. The return from system is headed for the supply on the primary.
Thanks for the confirmation guys. Guess I'll be finding a new HVAC contractor. Crazy.0
I can't see the volute of the secondary circ, but I think it's pumping at the x-tank.0
Arrow on the cast housing of the circ points away from the x-tank and towards the zone valves.0
Aside from the reversal of the close T's, someone mentioned a differential bypass... But since those are Grundfos Alphas, they remove the need for the bypass, right?0
They are not alpha's just regular 15-58 3 speed. If they were, then yes you would be correct.0
ah thanks for clearing that up. I don't know why I thought they were alphas.0