One pipe steam system adding cast iron base
Options
oopsplumber
Member Posts: 14
I understand I need to pipe it like a two pipe system. One supply and then a return connected to a wet return.
Two questions:
1. Do I need a steam trap?
2. I assume I need an air vent?
Two questions:
1. Do I need a steam trap?
2. I assume I need an air vent?
0
Comments
-
No steam trap needed, yes you need an air vent. You can also pipe the second pipe down a minimum of 5' then back up into the main, if you dont have a wet return. This creates a water seal and you won't get hammer.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
At the end of the original run right after the main vent the main the pipe run drops vertical about 5 feet then returns back to the boiler.
I am going to cut a tee in on that vertical drop about 3 feet below the main and have the bullnose pick up my radiator about 15 feet away.
Does this sound like an acceptable plan?
0 -
In that case, Where it is attached to that vertical drop, it has to be below the waterline.
0 -
Ok. Thanks
Last question:
Do I bring my supply in the top tapping on the rad or the bottom tapping opposite the return?0 -
Supply in the top, return out the opposite bottom end of the cast iron base,0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements